hello all ,
 ihope that you are all fine i will get into the point

i have two question
first

i need to know what is the difference between the high feature modiles and the standard modules and what is the meaning of high feature ?

second

i have HF AI modules with P.N ( 6ES7134-4LB02-0AB0) and i want to replace it by the Following Standard AI module with P.N ( 6ES7134-4GB00-0AB0)
is that possible or not ?
if no , why ?

if yes , will it affect the process??


thanks for your efforts

regards
Top
  6/24/2012, 10:42 PM
Joined 9/27/2006
Last visit: 6/19/2013
Posts: 4033
Rating:
Rated: Excellent [4.16 out of 5 / rated 622 time(s)]. (622) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello egy_eng;
Here is a FAQ that describes High-Feature modules:

New ET 200S High Feature Analog Modules with 0.5ms Cycle Time Released for Delivery

The following new functions were introduced:

  • Significantly faster cycle time of 0.5ms per module
  • Support of isochrone mode (interface module and DP master or PN IO controller must also support this function)
  • Support of I&M data (Identification & Maintenance, (interface module and DP master or PN IO controller must also support this function))
  • Process interrupt; If the upper or lower limiting values are exceeded (limiting values are freely  parameterizable)


If your system uses any one of these features you cannot replace the AI modules with an earlier version.

Hope this helps,
Daniel Chartier 




=== Edited by dchartier @ 6/24/2012 10:43 PM [GMT ] ===