Hello,

My new question is that, ok, I know that in digital output board there is the option when the plc goes to stop for a fault, we can configure each digital output for it is open or close, this option exist for analog out board, or something similar, or I use ob80 for example by I can do it.

thank you.

Top
  6/22/2012, 4:11 PM
Joined 4/24/2006
Last visit: 5/24/2013
Posts: 4679
Rating:
Rated: Excellent [4.12 out of 5 / rated 428 time(s)]. (428) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello David1981,

Do you use ET200S?
When you insert Analog output module, go to properties (parameters)
Here you can define "reaction to CPU/Master STOP" 
It can be :
- Output had no voltage
- Keep last value
- Substitute a value

Hope this will help