Thread Starter: Lucky123   Started: 6/22/2012 4:43 AM   Replies: 10

« Previous thread Next thread »
12» Page 1 of 2 (11 items)
  6/22/2012, 4:43 AM
Joined 12/20/2008
Last visit: 5/21/2013
Posts: 473
Rating:
Rated: Outstanding [3.37 out of 5 / rated 209 time(s)]. (209) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
in S7300 or 400 system, is there any module available which works Modbus over ethernet. The current CP341 module Modbus Serial work only with RS232, 422,485.

However, I did not find any module which works modbus over ethernet.
Top
  6/22/2012, 8:59 AM
Joined 4/10/2008
Last visit: 4/10/2013
Posts: 11
Rating:
Rated: Above avarage [3 out of 5 / rated 1 time(s)]. (1) 
Rated: Above avarage [3 out of 5 / rated 1 time(s)]. (1) 
You can use CP343 and 443 for modbus TCP/IP comm. You need 2XV9450-1MB00 license for one CPU, 2XV9450-1MB01 for redundant CPU's..
https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&objid=33118723&caller=view



=== Edited by ak11474 @ 6/22/2012 9:14 AM [GMT ] ===


Top
Thank you for this post from:
  6/22/2012, 4:34 PM
Joined 12/20/2008
Last visit: 5/21/2013
Posts: 473
Rating:
Rated: Outstanding [3.37 out of 5 / rated 209 time(s)]. (209) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Wonderful!

Thank you for the information. However, if I am already using CP443 for ethernet communication with the PC and 3rd party HMI, can I use the same CP443 for this modbus over ethernet, or I need to use any additional module.



=== Edited by Lucky123 @ 6/22/2012 4:36 PM [GMT ] ===


Top
  6/22/2012, 4:46 PM
Joined 11/27/2007
Last visit: 5/23/2013
Posts: 844
Rating:
Rated: Outstanding [3.88 out of 5 / rated 59 time(s)]. (59) 
Users with special expertise supervising conferences
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Hello Lucky,
yes, it is possible to run different protocols simultaneously via ethernet with one CP.

Regards,
Kaulquappe
Top
Thank you for this post from:
  6/22/2012, 8:58 PM
Joined 12/20/2008
Last visit: 5/21/2013
Posts: 473
Rating:
Rated: Outstanding [3.37 out of 5 / rated 209 time(s)]. (209) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thanks for the answer.

Do you have any example program for that?
Top
  6/24/2012, 9:17 AM
Joined 12/20/2008
Last visit: 5/21/2013
Posts: 473
Rating:
Rated: Outstanding [3.37 out of 5 / rated 209 time(s)]. (209) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Is there anyone have the example program using CP343 or CP443 for modbus over ethernet?
Top
  6/25/2012, 10:18 AM
Joined 9/22/2010
Last visit: 5/17/2013
Posts: 145
Rating:
Rated: Outstanding [3.74 out of 5 / rated 19 time(s)]. (19) 
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
If you take a look at the link that ak11474 posted before, you can find two usefull links:
1. To a side where you can download a demoversion that includes an example project
2. To an example application for Modbus TCP communication between a S7 PLC and a Modicon PLC

Regards
Sakura
Top
Thank you for this post from:
  6/25/2012, 7:11 PM
Joined 12/20/2008
Last visit: 5/21/2013
Posts: 473
Rating:
Rated: Outstanding [3.37 out of 5 / rated 209 time(s)]. (209) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thank you Sakura,

I got it now, I will try to look at the logic and code and see, if it helps.
Top
  7/10/2012, 11:26 AM
Joined 12/20/2008
Last visit: 5/21/2013
Posts: 473
Rating:
Rated: Outstanding [3.37 out of 5 / rated 209 time(s)]. (209) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I am told by Siemens Support that:

Siemens has a purchased product that supports Open Modbus/TCP ( 2XV9450-1MBxx ). However, the product is not supported in USA because the developer, IT4 Industry Erlangen Germany, had to create some custom code to support the communication.

Please do let me know, what's the solution for USA?
Top
  7/10/2012, 11:50 AM
Joined 11/27/2007
Last visit: 5/23/2013
Posts: 844
Rating:
Rated: Outstanding [3.88 out of 5 / rated 59 time(s)]. (59) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Lucky123 wrote:
I am told by Siemens Support that:

Siemens has a purchased product that supports Open Modbus/TCP ( 2XV9450-1MBxx ). However, the product is not supported in USA because the developer, IT4 Industry Erlangen Germany, had to create some custom code to support the communication.

Please do let me know, what's the solution for USA?

Hello Lucky,
as far as I know this ModbusTCP libraries are used in the USA as well. Do you mind that you will get support only in Germany?
What do you mean by "create some custom code"? Does this only apply for downloading the trial version?

Regards,
Kaulquappe