multiranger problem

Thread Starter: amar12   Started: 6/4/2012 6:12 PM   Replies: 3

« Previous thread Next thread »
Page 1 of 1 (4 items)
  6/4/2012, 6:12 PM
Joined 5/28/2012
Last visit: 6/6/2012
Posts: 6
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 


hello                                           Rnf:lblSmileyTooltip_

i have multiranger-200, but he seand this error message (losse echo), what means this message ?, what can i do?
bay the way i reed the manual, but i d'ont inderstend.
please helpe me.
thanks                   Rnf:lblSmileyTooltip_
Top
  6/6/2012, 2:15 AM
Joined 3/28/2010
Last visit: 5/24/2013
Posts: 122
Rating:
Rated: Excellent [4.43 out of 5 / rated 21 time(s)]. (21) 
Rated: Above avarage [3 out of 5 / rated 3 time(s)]. (3) 

Dan's Dozen - my list of LOE (Loss of Echo) causes:

1) Is the correct transducer model's code specified in P004?

2a) Location of transducer - see the transducer application manual for suggested locations, especially with respect to location next to a vertical wall and the effect of transducer location 'seeing' a dished (parabolic) bottom, whose echo will not reflect back.

3) Is surface that is reflecting an echo within the transducer's maximum range?  (A 6m transducer cannot 'see' 10m distance)

4) Aiming of transducer - it's aimed where it cannot return an echo. Re-aim.

5)  Transducer is overtightened in its threaded fitting.

6)  Excessive dust is attenuating the acoustic pulse and its echo.

7)  Something is in the blanking zone.

8a) Water or ice on the face of the transducer
     excessive water from shop air used for purge collects on xducer face

8b) Fog or condensed water when the dew point temperature drops below the tank's blanket atmosphere temperature.

9)  Carbon Dioxide (CO2) atmosphere.  Ultrasonic energy is absorbed like welfare checks by CO2.

10)  Faulty transducer with intermittent performance or a transducer affected by temperature change.

11)  LOE can be the result of attempting to read a dished bottom or when an open channel flow empties to zero (for the latter P801 is a range extension parameter).

12)  Are there 2 echoes arriving that can cannot be distinguised one from another? (echo profile needed)




=== Edited by danw @ 6/6/2012 2:16 AM [GMT ] ===


Top
Thank you for this post from:
  6/8/2012, 10:37 PM
Joined 9/25/2006
Last visit: 1/31/2013
Posts: 143
Rating:
Rated: Excellent [4.4 out of 5 / rated 5 time(s)]. (5) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dan,

I appreciate the "Dan's Dozen" but i would call it the "lucky thirteen" by adding one reason:

13) incorrect parameters / excessive applied TVT filtering...

cool

Regards,

SonicRanger.
Top
Thank you for this post from:
  6/28/2012, 7:56 PM
Joined 6/15/2009
Last visit: 4/3/2013
Posts: 73
Rating:
Rated: Outstanding [3.33 out of 5 / rated 3 time(s)]. (3) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello amart12

  You can help us to help you by giving us the follwoing values:

P807 (Noise)  read only
P806 Echo Strength
P805 Confidence

For 806 and 805, press the measure key at least 3 times with 10 seconds between each press and provide us an avergae reading.  The format will be xx:yy

Regards

Toppie  [ |:)
Top