Hello,

So, I start using WinCC Flex 2008 Sp3 with update 1 on my new window 7-64 bit machine. While transferring the project the 1st time on the MP377 with this new machine,it started updating the operating system ( as expected). But in the interim, the update stoped with an error message saying incompatible operating system.

And now I have a MP377, which will not boot up saying that the image is corrupt. I have tried to restore the backup image and go to factory setting, but I keep getting "interface error". I have tried making the transfer using MPI cable as well as ethernet and keep getting same error.

Also, I have a backup image on flash card, but how do I make the panel boot from the flash ?

Any suggestions would be appreciated.
Top
  5/21/2012, 9:45 PM
Joined 9/28/2005
Last visit: 5/15/2013
Posts: 2912
Rating:
Rated: Excellent [4.02 out of 5 / rated 208 time(s)]. (208) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

I suppose you've allready tried this What settings do you have to make on an MP 377 to reset the operator panel to the factory settings?
As long as your HMI is lets say 'dead', please power off it, configure Prosave as stated in that link, press 'Update OS' button and only the power on the HMI. If boot loader of HMI is still alive, you should be successful. Also, please make double and tripple check that you're using correct firmware version. Also, please tell me what do you see when power on the HMI ? Do you see any proof that bootloader is still alive ? It should stated at lest version of bootloader. If not, then I think you have big problems cry

Regards,
--------------------------------
Darius
Automation engineer/programmer
Top
  5/21/2012, 9:53 PM
Joined 3/18/2008
Last visit: 5/14/2013
Posts: 1058
Rating:
Rated: Outstanding [3.96 out of 5 / rated 175 time(s)]. (175) 
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
dipakkadam_619 wrote:
Hello,

So, I start using WinCC Flex 2008 Sp3 with update 1 on my new window 7-64 bit machine. While transferring the project the 1st time on the MP377 with this new machine,it started updating the operating system ( as expected). But in the interim, the update stoped with an error message saying incompatible operating system.

And now I have a MP377, which will not boot up saying that the image is corrupt. I have tried to restore the backup image and go to factory setting, but I keep getting "interface error". I have tried making the transfer using MPI cable as well as ethernet and keep getting same error.

Also, I have a backup image on flash card, but how do I make the panel boot from the flash ?

Any suggestions would be appreciated.


Hello dipakkadam_619,

Have you seen this FAQ?

What settings do you have to make on an MP 377 to reset the operator panel to the factory settings?

how do you do an operating system update (OS update) on operator panels?

if those FAQ doesnot help.

use 
Support Request
Top
  5/30/2012, 12:19 AM
Joined 11/4/2010
Last visit: 2/5/2013
Posts: 15
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Amit,Darius

Thank you for you replies and sorry I did not get a chance to reply sooner. So I had already tried the things that you asked me to do, but unfortunately did not work. Even with the factory reset, it would not communicate with the HMI at all. Seems like a corrupt operating system, so will have to send it in to Siemens to get repaired.

Thanks again Rnf:lblSmileyTooltip_
Top
Thank you for this post from:
  6/1/2012, 7:36 AM
Joined 3/18/2008
Last visit: 5/14/2013
Posts: 1058
Rating:
Rated: Outstanding [3.96 out of 5 / rated 175 time(s)]. (175) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
dipakkadam_619 wrote:
Hello Amit,Darius

 so will have to send it in to Siemens to get repaired.

Thanks again Rnf:lblSmileyTooltip_


i don't think that it will get repaired.

have you asked for replacement?

any way please revert back with result.Rnf:lblSmileyTooltip_
Top