Hello everybody,

The MM440 shows a Fault and is F0085, it's caused for External fault triggered via terminal inputs.

The remedy is "Disable terminal input for fault trigger", but I don't know how can I do this, What parameter I should change?


thanks so much, I appreciate your assistance
Top
  5/28/2012, 6:44 PM
Joined 7/8/2009
Last visit: 5/21/2013
Posts: 1167
Rating:
Rated: Excellent [4.24 out of 5 / rated 327 time(s)]. (327) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
This is programable fault

You have to check P2106 because value in P2106 is responsible for this fault

what is set in P2106?

The value of this Parameter should be one to avoid Tripping. You have to check value of this parameter and check why it is not 1 and is 0

If it is coming from FFBs, check Logic and if it is connected with DI, check termianl Input


Regards
Devesh



=== Edited by Vithani @ 5/28/2012 6:48 PM [GMT ] ===



Please say Thanks if your Problem is Solved.. :-)
Top
  5/28/2012, 6:50 PM
Joined 7/25/2011
Last visit: 5/8/2013
Posts: 47
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
the value of P2106 is 53.5 laugh
Top
  5/28/2012, 6:56 PM
Joined 7/8/2009
Last visit: 5/21/2013
Posts: 1167
Rating:
Rated: Excellent [4.24 out of 5 / rated 327 time(s)]. (327) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
JohanChala wrote:
the value of P2106 is 53.5 laugh


53.5 means f_act<=P2155 ( 0= NO, 1=Yes)

that value must be zero right now

That means Your actual frequency is crossing Limit set in P2155 and that causing drive to trip

Regards
Devesh

Please say Thanks if your Problem is Solved.. :-)
Top
  5/28/2012, 7:01 PM
Joined 7/25/2011
Last visit: 5/8/2013
Posts: 47
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I checked the value of P2106 and:

* at in000: 53.5
* at in001: 1
* at in002: 1

I don't know what mean this values because in the list of parameters doesn't explain sad
Top
  5/28/2012, 7:05 PM
Joined 7/25/2011
Last visit: 5/8/2013
Posts: 47
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thanks so much Vithani, I can see the problem Rnf:lblSmileyTooltip_ .
Top
  5/28/2012, 7:13 PM
Joined 7/8/2009
Last visit: 5/21/2013
Posts: 1167
Rating:
Rated: Excellent [4.24 out of 5 / rated 327 time(s)]. (327) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
JohanChala wrote:
I checked the value of P2106 and:

* at in000: 53.5
* at in001: 1
* at in002: 1

I don't know what mean this values because in the list of parameters doesn't explain sad


Ok Its good that you found problem Rnf:lblSmileyTooltip_

Was it crossing limit ? how you are going to rectify it? Please share with us all information so that other users facing same problem can get benifited

and, everything is in those manual Just you need to study them and read them as much as you can Rnf:lblSmileyTooltip_ Rnf:lblSmileyTooltip_ Rnf:lblSmileyTooltip_



=== Edited by Vithani @ 5/28/2012 7:14 PM [GMT ] ===



Please say Thanks if your Problem is Solved.. :-)