Technical Forum

MICROMASTER

shredder don't stop when is jam

Thread Starter: PCP Canada MS   Started: 5/28/2012 5:02 PM   Replies: 1

« Previous thread Next thread »
Page 1 of 1 (2 items)
  5/28/2012, 5:02 PM
Joined 12/6/2011
Last visit: 2/25/2013
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I make a aluminium junk shredder and i program the mm440 with this procedure http://support.automation.siemens.com/WW/view/en/16792191
but when the shredder is jam in the both direction the drive display the alarm A0501 and don't stop
so i want to know a cant program the drive the stop it after 4 or 5 rotation change or just stop when is jam and display fault and flashing a light.  the current limits is at 110% (P0640) and the value of P2170 is set to 80%


Top
  5/28/2012, 5:58 PM
Joined 7/8/2009
Last visit: 6/9/2013
Posts: 1170
Rating:
Rated: Excellent [4.24 out of 5 / rated 327 time(s)]. (327) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
You need to use FFBs if you want to Trip drive as you said

Please Refer following to set tripping parameters

FFB for tripping a MM440 VFD

MM440 NOT TRIPPING AT SUPPLYING THE MOTOR FULL CURRENT

Regards,
Devesh

I dont Like people driving Fast, thats the reason I overtake them ;)
Top
Page 1 of 1 (2 items)
Actions