Plz do as per the below steps,
1. 1. As per the axis stroke length create a compensation table.
Eg : If axis stroke length is from 0 to 500 mm
Make a interval measurement as per our wish for eg every 50 mm.
Therefore compensation table consists 11 points for this axis.
No of Table points = ((Axis stroke length / Interval)+1)
Enter Max Stroke =500 mm
Min Stroke = 0 mm
Step = 50 mm
2. 2. Then disable the Compensation enable parameter (Make it Zero).
3. 3. Then enter “0” in backlash parameter.
4. 4.Do the laser calibration with the help of Laser interferometer.
5. 5.In that first report you will get backlash value.
6.6. 6. Enter this backlash value in backlash parameter.
7. 7.Then do the calibration again and you will get pitch error value of the axis.
8. 8, Enter these values in corresponding table.
9. 9.Then Enable Compensation enable parameter (Make it One).
10. Then do the calibration again and check whether decrease or not.
If you have doubt in system accepting these error values or not means
You goto Diagnosis – Service display – Service axis - in that you are able to see the pitch error values in Absolute error compensation row.
Thanks......................