Communication / Networks
communication failure
Erstellt von Vini_ am 25.05.2012 11:57 (1 Antworten)

25.05.2012, 11:57
|
Beigetreten am: 14.08.2009
Letzter Besuch: 21.02.2013
Beiträge: 7
Bewertung:
(0)
|
(0)
|
If i want to get the energy values. I updated firmware to last one and i am not able to get any value neither in register 801 or 2801. I have communication failure. I am using the next ones with a MODBUS opc server (OFS FROM SCHNEIDER) MW801 MW802 MF801 MF802 MD801 MD802
Which is the good register taking into accound the offset. Regards
|
|
|
|

25.05.2012, 14:08
|
Beigetreten am: 27.11.2007
Letzter Besuch: 21.05.2013
Beiträge: 839
Bewertung:
(58)
|
(0)
|
Hello Vini, if the Schneider OPC server uses address 40001 for the first holding register, you should add 40001 to 801 (if that is the PAC register you'd like to read).
Regards, Kaulquappe
|
|
|
|