SINAMICS
fault-30022 in sinamics s-120 drive
Erstellt von vivekbhavsar am 25.05.2012 11:09 (4 Antworten)

25.05.2012, 11:09
|
Beigetreten am: 18.04.2012
Letzter Besuch: 17.05.2013
Beiträge: 20
Bewertung:
(0)
|
(0)
|
Dear all,
I faced fault-30022 in sinamics drive which having simotion M-D435 and CU-320.what causes are responsible for this fault and how can i solve this fault please gauide me regardig to this.
Regards,
Vivek
|
|
|
|

25.05.2012, 11:37
|
Beigetreten am: 14.09.2007
Letzter Besuch: 09.04.2013
Beiträge: 33
Bewertung:
(2)
|
(1)
|
Dear Vivek,
Fault F30022 is basically for for defect in IGD card or short ckt or open the IGBT.you can check the IGBT with the help of multimeter with the help of attached file. Mostly i found problem with IGD or IGBT.
Regrads, Shank
|
|
|
|

25.05.2012, 12:25
|
Beigetreten am: 18.04.2012
Letzter Besuch: 17.05.2013
Beiträge: 20
Bewertung:
(0)
|
(0)
|
Dear shnak,
Actually I have no idea that how to perform the cold test of igbt? could u tell me before performing this test which connections i have to removed? is it possible any other reason is responsible for this fault-30022.?
Regards, Vivek
|
|
|
|

25.05.2012, 13:26
|
Beigetreten am: 14.09.2007
Letzter Besuch: 09.04.2013
Beiträge: 33
Bewertung:
(2)
|
(1)
|
Dear Vivek,
Remove the motor outgoing connection & DC link or Incoming AC supply connection . Switch OFF the Control as well as 24 VDC supply & then carried out cold run test. Normally if you check the fault causes it is due to damage of fibre optic cable or power cable connection opened, or otherwise because of IGD card or IGBT failure.
Regards, Shank
|
|
|
|

28.05.2012, 10:15
|
Beigetreten am: 18.04.2012
Letzter Besuch: 17.05.2013
Beiträge: 20
Bewertung:
(0)
|
(0)
|
Dear shank, Thanx your given information is very helpful.......
|
|
|
|
Aktionen