Trend value mismatch on Redundant Servers

Thread Starter: R J   Started: 12/12/2011 10:23 AM   Replies: 3

« Previous thread Next thread »
Page 1 of 1 (4 items)
  12/12/2011, 10:23 AM
Joined 10/20/2009
Last visit: 5/15/2013
Posts: 129
Rating:
Rated: Excellent [4.25 out of 5 / rated 4 time(s)]. (4) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi to all,

Currently i am working on "PCS7 V6.1 Sp3". We have established redundant server & client architecture in plant. Time synchronisation is also established between redundant server's, clients & CPU 414-2H.

We are capturing trends on both servers but it showing "different values at the same time instance" whenever the surge occurs in the process for particular process parameter. How to resolve this problem? Kindly provide the solution.

Regards,
R J
===================================
Your ‘I CAN’ is more important than your ‘I.Q’
Top
  12/12/2011, 3:02 PM
Joined 10/26/2011
Last visit: 5/21/2013
Posts: 265
Rating:
Rated: Excellent [4.63 out of 5 / rated 41 time(s)]. (41) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Hello R J

Did you check if the archives of booth servers are synchronized? And have the same values?
Do they have the same PC time? Is the time synchroniszation OK?

If the time synchronisation is running without mistakes and the archives are synchronized, the values must be the same.

Regards


With best regards,
Thunderstorm
Top
  12/13/2011, 2:07 PM
Joined 9/29/2009
Last visit: 4/25/2013
Posts: 42
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi RJ,
     Just check the if you are using COM cable for data sync between two servers.

If using then check:
1. Also check the settings in your wincc if this feature is enabled.

2. If you are using the  COM cable just check it once again for proper functioning.

Rnf:lblSmileyTooltip_

Thanks 
AGR 
Top
  5/18/2012, 5:25 PM
Joined 10/20/2009
Last visit: 5/15/2013
Posts: 129
Rating:
Rated: Excellent [4.25 out of 5 / rated 4 time(s)]. (4) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi AGR,

Thanks for reply.

I have check all the things you mentioned & everything is right.

Somehow i have solved this problem by installing latest hotfix 31 of PCS7 V6.1 SP4

Regards,
R J
===================================