When i go online to me simodrive unit via Profibus it only displays Drive A no Drive B on the LED display It has the alarm E-B799 i go through the usual process of saving to the FEPROM and doing a power of restart the fault still remains was hoping to see more information through the Simocom U Software but again it does not display any info reguarding the B Drive. Any help Please.
Hi.
If I understand you correctly.
I think you have changed between the control board is a uniaxial two-axis power module and the drive. So you have an error in drive B uniaxial power module. You do not see the drive B, because single-axis power module.
You will need: Menu "Option"->"Service"->"Delete drive configuration".
You remove the memory drive data on both drives (Drive A and Drive B). Next you need to parameterize the drive A again.
Best regards.