How to convert and corrto signal 4-20mA to 0-20mA
because I have two sensors that are 4-20mA and S7-1200 has only inputs 0-20mA how should I proceed in this case



=== Edited by O_Moderator @ 4/24/2012 11:02 AM [GMT ] ===
new subject after splitting from Share Samples and Tips Application for PLC S7-1200 & TIA PORTAL

Top
  4/23/2012, 7:42 AM
Joined 10/17/2009
Last visit: 6/12/2013
Posts: 112
Rating:
Rated: Outstanding [4 out of 5 / rated 3 time(s)]. (3) 
Martin,do not post questions here. Make a new thread.
Top
  4/23/2012, 11:16 PM
Joined 8/31/2010
Last visit: 6/19/2013
Posts: 1267
Rating:
Rated: Outstanding [3.88 out of 5 / rated 106 time(s)]. (106) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Martins_Eng wrote:
How to convert and corrto signal 4-20mA to 0-20mA
because I have two sensors that are 4-20mA and S7-1200 has only inputs 0-20mA how should I proceed in this case


Hello Martins_Eng,
You can make use of the 0-20mA channel to read the 4-20mA signal also. The value below 4 mA would be displayed as 0.

Like it? Rate it!
Top
  4/24/2012, 11:20 AM
Joined 12/1/2009
Last visit: 6/11/2013
Posts: 322
Rating:
Rated: Outstanding [3.57 out of 5 / rated 28 time(s)]. (28) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Martins_Eng,

here is the solution:

https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=39334504&objAction=csOpen&nodeid0=41885258&lang=en&siteid=cseus&aktprim=0&extranet=standard&viewreg=WW

Regards.

-------------------------------------------------------------------------------------------------------
Give us your feedback and show us your respect!
We take our free time to support you with our knowledge and experience.
If this post is helpfull to you kindly click on "Rate" or "Thank".
Top
  4/24/2012, 11:31 AM
Joined 1/3/2012
Last visit: 7/3/2012
Posts: 12
Rating:
Rated: Very Good [2 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Martins_Eng,

Use don't need to convert a 4-20mA signal to 0-20mA. Use the 0-20mA channel to read the 4-20mA signal.

Take a look to the tuturial that I attached to this post (Analog Value Processing).

Attachment: EN_M05_S7-1200_analog.pdf  (118 Downloads)

***** Portuguese Siemens Lover *****

Top
Thank you for this post from:
  4/25/2012, 12:57 PM
Joined 7/24/2008
Last visit: 6/20/2013
Posts: 2084
Rating:
Rated: Excellent [4.3 out of 5 / rated 363 time(s)]. (363) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

you can found also ready to use blocks to your case in
https://www.automation.siemens.com/WW/forum/guests/PostShow.aspx?PageIndex=1&PostID=150327&Language=en&onlyInternet=False#top

Denilson Pegaia
Siemens Industry Sector
Industry Automation and Drive Technologies Division
- Technical Support & Hotline -
Rua Werner Siemens, 111
05069-900 São Paulo
Hotline – Atenção ao Cliente
Tel.: +55 11 3833-4040
E-Mail: atencao.cliente.ac.br@siemens.com
Homepage Brasil: www.siemens.com.br
Manuais / FAQ’s / Downloads: http://www.Siemens.com.br/Servicos&Suporte
Top
Thank you for this post from:
  5/17/2012, 6:25 PM
Joined 7/17/2010
Last visit: 6/11/2013
Posts: 160
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thanks guys
Top
Page 1 of 1 (7 items)
Actions