MAG5000 loses pulse signal output
Erstellt von titan84 am 02.05.2012 07:03 (4 Antworten)

02.05.2012, 07:03
|
Beigetreten am: 07.10.2009
Letzter Besuch: 10.06.2013
Beiträge: 48
Bewertung:
(0)
|
(0)
|
Hi every body! Now, my transmitter- MAG5000 ( order no.: 7ME6910-1AA30-1AA0) was be error. Detail: + the pulse signal output doesn’t work so i can't receive the pulse signal to count the flow. + The current output is still ok. I still receive current signal on my PLC. How is my transmitter error? How solve the problem?
|
|
|
|

02.05.2012, 07:54
|
Beigetreten am: 13.06.2006
Letzter Besuch: 15.04.2013
Beiträge: 186
Bewertung:
(6)
|
(0)
|
Hi,
You need a verificator to test the magflo meter, if you don't have this equipment, you have to send your transmitter back to Siemens for checking or repair.
Regards, Chook
|
|
|
|

02.05.2012, 09:40
|
Beigetreten am: 07.10.2009
Letzter Besuch: 10.06.2013
Beiträge: 48
Bewertung:
(0)
|
(0)
|
Is the Connection board ( order no: A5E0255981) reason? Can i exchange the connection board?
|
|
|
|

03.05.2012, 02:24
|
Beigetreten am: 13.06.2006
Letzter Besuch: 15.04.2013
Beiträge: 186
Bewertung:
(6)
|
(0)
|
Hi,
You have to make a visual inspection of connection board, but this board is very hard to get damage unless the surface mount components blow up onto the PCB due to your power surge damage happened.
You aslo check the pins of PCB connector to ensure the pins are not bended.
Connection board for polyamide terminal box 24 Vdc, new part number is A5E02559817
Regards Choock
|
|
|
|

09.07.2012, 02:27
|
Beigetreten am: 02.09.2010
Letzter Besuch: 22.05.2013
Beiträge: 3
Bewertung:
(0)
|
(0)
|
-->First check if pulse o/ps are enabled -->Are you using active or passive o/p? if they are enabled double check with your multimeter,you will see that values are jumpimh up and donw. -->use resistors as indicated in manual other wise it will not work
|
|
|
|