Process Control System - APACS+
upgrade ACM(VERSION 3) TO ACM+(VERSION 4)
Thread Starter: HAMPEL Started: 9/19/2011 3:15 PM Replies: 1

9/19/2011, 3:15 PM
|
Joined 9/19/2008
Last visit: 11/6/2011
Posts: 11
Rating:
(0)
|
(0)
|
1.HOW CAN I UPGRADE ACM TO ACM+?
2.IF I CHANGE SECONDARY CPU IN REDUNDANCY MODE WITH NEW CPU,THIS CPU AUTOMATICALY WILL COMMITIONED WITH PRIMARY CPU?
3.IN CASE OF 2 IF MY CPU IS NOT EMPTY:IS IT CORRECT I CHANGE WITH SECONDARY CPU? & WHAT HAPPENED AFTER THIS ACTION?
|
|
|
|

4/30/2012, 6:59 PM
|
Joined 12/20/2005
Last visit: 4/23/2013
Posts: 78
Rating:
(3)
|
(0)
|
1.HOW CAN I UPGRADE ACM TO ACM+? Assuming you have the hardware already, in 4-mation create a new offline ACM+ configuration. Do not initialize (double-click) the module yet, leave it "yellow" in the module tree. Export your existing ACM configuration. Import teh expoted ACM file into the new ACM+. Review\resolve any errors or warnings. You can then transfer teh newly created offline ACM+ to the controller online (ACM+).
2.IF I CHANGE SECONDARY CPU IN REDUNDANCY MODE WITH NEW CPU,THIS CPU AUTOMATICALY WILL COMMITIONED WITH PRIMARY CPU? I would not attempt this on a running plant. The best way to handle is to do it when teh plant is offline then remove both old ACMs, install one new ACM+. Allow the new one to initialize, then add the redundant partner.
3.IN CASE OF 2 IF MY CPU IS NOT EMPTY:IS IT CORRECT I CHANGE WITH SECONDARY CPU? & WHAT HAPPENED AFTER THIS ACTION? I would not attempt this.
Contact Tech Support if you need to talk this through with someone.
Good luck, RJP
|
|
|
|