Hello,
Be aware that the F-switch is a failsafe module.
You must also configure the CPU to hold a safety program (see "Protection" Tab in the CPU properties, ==> check the boxes "can be bypassed with password" and "CPU contains safety program"
Make sure that the address switch setting of the F-I/O matches the PROFIsafe destination address in STEP 7 HW Config (Parameter "F_Destination_Address").
The F_destination_address is shown in binary format in the "DIP switch setting" parameter in
the object properties for the fail-safe modules in HW Config . You must obtain this PROFIsafe address from the parameter assignment dialog box and set it on the fail-safe modules using
an address switch.