PAC3200 Modbus TCP Issue
Erstellt von dtv am 20.04.2012 14:57 (2 Antworten)

20.04.2012, 14:57
|
Beigetreten am: 20.04.2012
Letzter Besuch: 10.02.2013
Beiträge: 1
Bewertung:
(0)
|
(0)
|
Hi,
I have just tried to connect to a SENTRON PAC3200 via Modbus TCP. I am not able to connect at all. With the SENTRON powerconfig it is possible to connect with the SEAbus TCP protocol, but not with Modbus TCP. I have tried several Modbus Test Programs, but it seems that the TCP connection is refused. However I can ping the device over the LAN. Is there any special setting required (TCP Settings)?
|
|
|
|

26.04.2012, 15:51
|
Beigetreten am: 28.04.2011
Letzter Besuch: 07.05.2013
Beiträge: 5
Bewertung:
(0)
|
(0)
|
Hi.
Check your PAC3200 communication settings for "Modbus TCP" protocoll in your device (page 21.6)
|
|
|
|

26.04.2012, 16:13
|
Beigetreten am: 27.11.2007
Letzter Besuch: 17.05.2013
Beiträge: 838
Bewertung:
(58)
|
(0)
|
Hello dtv, the client must use remote port 502 and the UNIT must not be 0.
Regards, Kaulquappe