Technical Forum

SIMOTICS

how torque is controlled in Vector Control mode

Thread Starter: Import-User-1   Started: 4/18/2012 1:14 PM   Replies: 3

« Previous thread Next thread »
Page 1 of 1 (4 items)
  4/18/2012, 1:14 PM
Joined 8/10/2005
Last visit: 6/19/2013
Posts: 3063
Rating:
Rated: Outstanding [3.12 out of 5 / rated 17 time(s)]. (17) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Mothilal wrote:
hi Vithani

    I have one fundamental doubt in drives... In vector control , how do you independently control the torque producing current and flux producing current in an INDUCTION MOTOR? 

  ' If you give the supply voltage  to the motor winding, the motor draws a required current depending on winding impedance. Then how do you control the current independantly? Both active and reactive current are flowing in the same winding ( due to the PWM inverter supply voltage).. 

Vector control is only for operating the motor at setpoint torque value? or It operates the motor at specified setpoint speed and specified setpoint torque? (i.e for example 2 Nm at 150 rpm and 2 Nm at 500 Rpm)

  In VC drives, How do u adjust the motor input voltage and frquency  to control the reactive and active current independently?

  Please clarify my doubt if u have any idea...

Thanks

Regards

Top
  4/18/2012, 1:16 PM
Joined 8/10/2005
Last visit: 6/6/2013
Posts: 1471
Rating:
Rated: Excellent [4.19 out of 5 / rated 21 time(s)]. (21) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Vithani wrote:

Please refer following Link

 Electric motors, generators & controls engineering Forum at Eng-Tips

I hope this will make you clear

Top
  4/19/2012, 6:25 AM
Joined 11/30/2011
Last visit: 3/12/2013
Posts: 164
Rating:
Rated: Above avarage [3 out of 5 / rated 21 time(s)]. (21) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
one more answer:

This explanation is given by PISCEAN 2010:


" in case of sensor less vector control drives during tuning, drive calculates the no load current or magnetization current of motor. Generally this is known as no load current. When motor is loaded, drive measures the actual current drawn by motor. If the drive is configured as torque set point it will try to keep current constant. (As drive know the magnetization current, rest thing is it simply tries to keep other i.e. load current constant) If the measured current starts dropping it just busts & keeps the load current constant. This is how sensor less VC drives works.Hope I am able to clarify your doubts"

Regards

Mothilal

***ALL IS WELL***
Top
  4/19/2012, 1:19 PM
Joined 7/8/2009
Last visit: 6/20/2013
Posts: 1180
Rating:
Rated: Excellent [4.24 out of 5 / rated 327 time(s)]. (327) 
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Import-User-2 wrote:
Vithani wrote:

Please refer following Link

 Electric motors, generators & controls engineering Forum at Eng-Tips

I hope this will make you clear



Corrected Link is

http://www.eng-tips.com/faqs.cfm?fid=1062

Please have a look on that

Its very nice explanation on VC

Regards
Devesh Vithani

I dont Like people driving Fast, thats the reason I overtake them ;)
Top
Thank you for this post from:
Page 1 of 1 (4 items)
Actions