Dear Expert,
Hi, I'm using a CPU 317F-2PN/DP and how to get rid off the BF and SF this two LED remain red when the plant is running..

Thanks
Top
  4/13/2012, 1:20 AM
Joined 9/27/2006
Last visit: 6/17/2013
Posts: 4029
Rating:
Rated: Excellent [4.16 out of 5 / rated 622 time(s)]. (622) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Tevita;
Your first reflex should always be to check the contents of the CPU's Diagnostic Buffer whenever the BF (Bus Fault: problem on the network) and the SF (System Fault: internal problem, in the configuration or the programming) appear.
AS the CPU continues running, I would presume that the diagnostic OBs (OB83, OB85, OB86..., OB122) are present in your program file, so you should have good information on what the PLC is complaining about.
If you have trouble understanding the messages, you can save the contents of the Diagnostic Buffer and upload them to the forum, so we can help decypher it.
Hope this helps,,
Daniel Chartier
Top
  4/13/2012, 3:29 AM
Joined 4/4/2012
Last visit: 2/7/2013
Posts: 12
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,
Here are the message from the Diagnostic Buffer.
                   Details on Event.         Event ID: 16# 38C4
Distributed I/O: station return.
Address of the affected DP slave: station number 81.
DP master system IO: 1
Log base address of the DP slave: input adress 8081.
Log base address of the DP master: 8191.
Requested OB: Rack failure OB(OB 86).
Priority class: 23
External error,incoming event

Thanks
Top
  4/13/2012, 3:57 AM
Joined 4/30/2008
Last visit: 6/17/2013
Posts: 640
Rating:
Rated: Outstanding [3.92 out of 5 / rated 37 time(s)]. (37) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
check node 81 on your profibus.check your connections ,end of line termination resistor, power to the node

Regards


Steve

Do yourself a favour
Read the manual
try the search function
then ask
Top