Hello, I'm working with FM 458 and sometimes i get this fault on FM by running system:
Informations in the exception buffer Informations concerning the last crash: Time of day: 26.11.11 19:55:27.5433 h ID: #4 USER Supplementary ID: 54 (User STOP triggered on this CPU)
I can not find this fault code in help. Have you any idea? Pls Thanx
=== Edited by miskopeter @ 2/27/2012 1:36 PM [GMT ] ===
|
|
|
|
|

2/27/2012, 1:49 PM
|
Joined 8/25/2006
Last visit: 5/19/2013
Posts: 898
Rating:
(85)
|
(0)
|
Hello. This is generally not a fault. This is message about that the execution of program was stopped by the user at mentioned date/time. This may be done using CFC command 'CPU-Operating mode-Stop', or may be in Simatic Manager 'PLC-Module Information' (if I remember correctly).
|
|
|
|

2/27/2012, 2:52 PM
|
Joined 4/27/2010
Last visit: 4/5/2013
Posts: 8
Rating:
(0)
|
(0)
|
Hello i had the same opinion but line is normally working and this fault i will get after few hours - nobody is touching the system
|
|
|
|

2/27/2012, 5:57 PM
|
Joined 8/25/2006
Last visit: 5/19/2013
Posts: 898
Rating:
(85)
|
(0)
|
How often do you see this 'fault'? Every day, every few hours? What is on the first tab of 'Module Information'? Are you sure that nobody touch the FM458?
|
|
|
|

2/28/2012, 7:27 AM
|
Joined 4/27/2010
Last visit: 4/5/2013
Posts: 8
Rating:
(0)
|
(0)
|
Last 3 days two times. On first tab are no errors.
Display of the system error panels SYS_ERR and INIT_ERR:
Initial error: 0x0000 -> no initial error registered Initialization error: 0x0000 PN-Init. and PN-IB error: 0x0000 Coordination error during Init.: 0x0000 Missing reply from the C bus: 0x0000 Missing reply from the L bus: 0x0000 Error during $ signal init.: 0x0000 Task manager error T1: 0x00 Task manager error T2: 0x00 Task manager error T3: 0x00 Task manager error T4: 0x00 Task manager error T5: 0x00 Aufgabenverwalter-Fehler I1: 0x00 Aufgabenverwalter-Fehler I2: 0x00 Aufgabenverwalter-Fehler I3: 0x00 Aufgabenverwalter-Fehler I4: 0x00 Aufgabenverwalter-Fehler I5: 0x00 Aufgabenverwalter-Fehler I6: 0x00 Aufgabenverwalter-Fehler I7: 0x00 Aufgabenverwalter-Fehler I8: 0x00 HW monitoring error: 0x00000000 User error: 0x0000 Communication error: -> no error registered Hardware errors (INIT_ERR): -> no error registered ----------------------------- End of Diagnosis -------------------------------
|
|
|
|

2/28/2012, 9:42 AM
|
Joined 8/25/2006
Last visit: 5/19/2013
Posts: 898
Rating:
(85)
|
(0)
|
Hello. When you have message in the exception buffer does your FM-program runs or not at this time? What do you see in 'Module Information' called from Simatic Manager? In Simatic Manager right-click on FM458 and select PLC-Module Information. Do you see here events with numbers AF06 or AF0C and after it AF03?
|
|
|
|