Dear all,
I have 6 (six) CPU214 (6ES7214-1AD23-0XB0) then I want to read specific value for each CPU with WinCC Flex Runtime. Distance between WinCC Flex Runtime and CPU214 is about 50 meters. So.... Can I used PC Adapter USB (6ES7972-0CB20-0XA0) instead CP5611?

Thx all grin
Top
  2/6/2012, 8:24 AM
Joined 4/22/2010
Last visit: 6/19/2013
Posts: 3309
Rating:
Rated: Excellent [4.12 out of 5 / rated 300 time(s)]. (300) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Have a look at the manual http://support.automation.siemens.com/WW/view/en/1109582
Chapter 7 and this S7-200 CPUs -- Configuring and programming communication -- Configuring communication to PCs 

Regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!
Top
  2/6/2012, 10:23 AM
Joined 8/31/2010
Last visit: 6/14/2013
Posts: 1267
Rating:
Rated: Outstanding [3.88 out of 5 / rated 106 time(s)]. (106) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rizal Listio wrote:
Dear all,
I have 6 (six) CPU214 (6ES7214-1AD23-0XB0) then I want to read specific value for each CPU with WinCC Flex Runtime. Distance between WinCC Flex Runtime and CPU214 is about 50 meters. So.... Can I used PC Adapter USB (6ES7972-0CB20-0XA0) instead CP5611?

Thx all grin

Helo Rizal Listio,
You can use CP5621 (PCI Express 32-bit) in place of CP5611. Since CP5711 has only a USB cable connected to the PC, compared to the permanent connection of CP5623 CP5621 to the PC.



=== Edited by Ganes10 @ 2/6/2012 12:46 PM [GMT ] ===
changed CP5623 to CP5621


Like it? Rate it!
Top
  2/6/2012, 12:37 PM
Joined 2/6/2012
Last visit: 2/8/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Ganes10 wrote:
Rizal Listio wrote:
Dear all,
I have 6 (six) CPU214 (6ES7214-1AD23-0XB0) then I want to read specific value for each CPU with WinCC Flex Runtime. Distance between WinCC Flex Runtime and CPU214 is about 50 meters. So.... Can I used PC Adapter USB (6ES7972-0CB20-0XA0) instead CP5611?

Thx all grin

Helo Rizal Listio,
You can use CP5621 (PCI Express 32-bit) in place of CP5611. Since CP5711 has only a USB cable connected to the PC, compared to the permanent connection of CP5623 to the PC.


but is it possible to use 6ES7901-3CB30-0XA0 (Intelligent RS232/PPI cable with built-in RS232/RS485 converter) or 6ES7901-3DB30-0XA0 (Intelligent USB/PPI cable with built-in USB/RS485 converter) instead CP5621? because CP5621 is quite expensive sad
Top
  2/6/2012, 12:53 PM
Joined 8/31/2010
Last visit: 6/14/2013
Posts: 1267
Rating:
Rated: Outstanding [3.88 out of 5 / rated 106 time(s)]. (106) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rizal Listio wrote:

but is it possible to use 6ES7901-3CB30-0XA0 (Intelligent RS232/PPI cable with built-in RS232/RS485 converter) or 6ES7901-3DB30-0XA0 (Intelligent USB/PPI cable with built-in USB/RS485 converter) instead CP5621? because CP5621 is quite expensive sad

Hello Rizal Listio,
Both the cables you mentioned are intended for downloading projects / Going online (diagnostics). Whereas you requirement is communicating CPU's with WinCC Flexible RT Advanced with also a distance of 50m.
So you need to go for CP to have a deterministic / stable communication for 24x7 operations.

Like it? Rate it!
Top
  2/6/2012, 1:00 PM
Joined 3/21/2006
Last visit: 6/19/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Basically you can to use them. But 50m isn't so far?
Arunakat1 wrote:

Hello,

Well I have done this few times without problem. I had made a cable myself. Actually what I does is I extend the rs 485 side of the PPI cable using two D connectors (male and female and connect all pins one to one parallel).

But be care full sometimes if the distance is too long or is there is some interference then you can see some crazy things printing. blink

Best regards.



Best regards,
Hristo Mihalev



=== Edited by UMENCHO @ 2/6/2012 1:01 PM [GMT ] ===


Top
  8/9/2012, 8:29 AM
Joined 10/7/2009
Last visit: 6/14/2013
Posts: 22
Rating:
Rated: Above avarage [3 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
WinCC Flexible Runtime can not comminicate with S7-200 via USB/PPI Multi-Master Cable (6ES7 901-3DB30-0XA0). You should use RS232/PPI Multi-Master Cable (6ES7 901-3CB30-0XA0) instead.
Top