Dear friends,

I have referred to the CP243-2 AS-i module, I tried to know what is the maximum number of slaves that can attached to this module but unfortunately i have failedcry.
Please help.

Regards.
Tomy.

Aim Higher
Top
  12/5/2011, 12:52 PM
Joined 4/22/2010
Last visit: 5/21/2013
Posts: 3191
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Users with special expertise supervising conferences
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Hello Tomy,

31 in standard addressing mode, 62 in extended adressing mode.

More information http://support.automation.siemens.com/WW/view/en/2659515?Datakey=24283631
And http://support.automation.siemens.com/WW/view/en/26250840

Regards,

Marcjan



=== Edited by Marcjan @ 12/5/2011 12:56 PM [GMT ] ===



Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!
Top
  12/8/2011, 12:42 PM
Joined 11/26/2011
Last visit: 1/11/2012
Posts: 27
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi!

At the beginning the maximun number of slaves in ANY ASI network was 32, but with the new ASI profiles there are A and B slaves, so then you can have 32x2=64. 

Saying that you can have 64 slaves is not 100% true, since there are slave modules that use A&B as analog input/outputs or 8DI modules; and then the maximum number is reduced.

It´s more accurate to say that you can have 32A slaves and 32B slaves, and when any module uses the A and B slave number it uses 2 slaves.

Why internet was not available when I began to work with plc's?
Two days to solve a problem with a cable, jajaja
www.SiemensLogo.com
Top
  12/8/2011, 2:22 PM
Joined 4/22/2010
Last visit: 5/21/2013
Posts: 3191
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Users with special expertise supervising conferences
Rated: Above avarage [3 out of 5 / rated 1 time(s)]. (1) 
Hello,

The links i provided tell a different story about maximum slaves on 1 master (in case of the CP243)
Or do i understand this text wrong?

wrote:

The CP 243-2 supports all the functions defined in the extended AS-Interface specification

V2.1, which means that dual address assignments (A-B) allow up to 62 digital or 31 analog

slaves to be operated on the AS-Interface.

sad

Of course you are right about the analog slave using 2 (A+B) adress assignments.

Regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!
Top
  12/9/2011, 2:18 PM
Joined 11/26/2011
Last visit: 1/11/2012
Posts: 27
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Sorry for the mistake! Rnf:lblSmileyTooltip_

I used my fragile memory to say 32 slaves, the max number is 31, and because the address 0 can´t be used it gives 31 slaves.

Although documentation says 31 analog slaves or 64 digital slaves, there are digital slaves that use A+B address too; and it´s more accurate to say from 31 to 64 depending on the slaves in the system as they can be mixed. In the same net you can have digital & analog using A,B or A+B.

Thanks for the correction Rnf:lblSmileyTooltip_

Why internet was not available when I began to work with plc's?
Two days to solve a problem with a cable, jajaja
www.SiemensLogo.com
Top
Thank you for this post from:
  12/9/2011, 2:40 PM
Joined 4/22/2010
Last visit: 5/21/2013
Posts: 3191
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Yes, i agree the manual is not completly clear about the amount of slaves.


So thank you for adding that information.Rnf:lblSmileyTooltip_

Regards,

Marcjan

 



=== Edited by Marcjan @ 12/9/2011 2:58 PM [GMT ] ===
something messed up


Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!
Top