Technical Forum

SIMATIC S7-200

TD 400C compatibility with CPU21x

Thread Starter: Mark_F   Started: 12/7/2011 9:24 PM   Replies: 3

« Previous thread Next thread »
Page 1 of 1 (4 items)
  12/7/2011, 9:24 PM
Joined 8/22/2011
Last visit: 6/11/2013
Posts: 30
Rating:
Rated: Outstanding [4 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

So my question is - is the TD 400C compatible with older S7-200 CPUs? 

I'm currently trying to connect CPU215 to TD 400C but the program won't download after I use the TD wizard. Compiler shows no errors but when I try to download this message appears:

"A compile error occured, check non-fatal errors for more information."

 

CPU is 215 release 01.00

and TD is TD 400C version 2.0.0.4

 

Thanks in advance for any kind of info




=== Edited by Mark_F @ 12/7/2011 9:24 PM [GMT ] ===


Top
  12/8/2011, 3:53 AM
Joined 7/24/2006
Last visit: 6/20/2013
Posts: 1844
Rating:
Rated: Outstanding [3.68 out of 5 / rated 217 time(s)]. (217) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

have you checked the non-fatal errors?

I do not belive that the TD400C will work with a ols 21x PLC. On a 215 it will never work on Port 1 because this is the the DP-Port.

Good luck

Helmut
Top
  12/8/2011, 7:52 AM
Joined 7/4/2011
Last visit: 2/18/2013
Posts: 15
Rating:
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 

hi,

try to delete "TD_ALM_0" sub program under program block->wizard in the project tree and download it again...

BR
sankar

Top
Thank you for this post from:
  12/8/2011, 12:15 PM
Joined 8/22/2011
Last visit: 6/11/2013
Posts: 30
Rating:
Rated: Outstanding [4 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Sankar NS wrote:


hi,

try to delete "TD_ALM_0" sub program under program block->wizard in the project tree and download it again...

BR
sankar



Hi,

this really helped. Luckily I don't need alarms for this configuration.



Thank you very much Sankar.

Helmut_13 wrote:
Hi,

have you checked the non-fatal errors?

I do not belive that the TD400C will work with a ols 21x PLC. On a 215 it will never work on Port 1 because this is the the DP-Port.

Good luck

Helmut


Hi,

but it works (on Port 0). I'll see how it behaves but for now I see no problems.
If something occurs I'll report here in the thread.

Thanks for your answer.



=== Edited by Mark_F @ 12/8/2011 12:16 PM [GMT ] ===


Top
Page 1 of 1 (4 items)
Actions