                    Here i have used siemens make Y-Link with ABB DCS for communicating the third party control device.


I have gsd files for third party control device.

But I want to know gsd file required for Y-link to configured in ABB DCS or it will detect by automatically?.


Kindly give us solution Thanks in advance...


“Change will not come if we wait for some other person or some other time. We are the ones we have been waiting for. We are the change that we seek”
Top
  10/25/2011, 1:08 AM
Joined 9/27/2006
Last visit: 5/19/2013
Posts: 3928
Rating:
Rated: Excellent [4.15 out of 5 / rated 619 time(s)]. (619) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Ganesan;`
Consider this: you can use a Y-Link (a Y-coupler connected to a pair of IM 153-2 interface modules) on a S7-400H system, in order to maintain redundancy between the CPUs and the Profibus-DP remote I/O.
However, you cannot use a Y-Link when the redundancy is done through Software redundancy, even if the 2 redundant CPUs are S7-400 PLCs, or if they are S7-300 PLCs. Only the Siemens  H-CPUs have the adequate software/hardware combination to support a Y-Link.
Now, do you think your ABB redundant system could possibly have the adequate software/hardware combination to handle I/O redundancy over a Y-Link, if non-redundant Siemens PLCs cannot?
I am afraid you are going to have to look for a solution based on ABB hardware. Maybe someone with more experience with these can give you pointers, unfortunately I do not have any knowledge of any such.
Hope this helps,
Daniel Chartier