Thread Starter: menfarhat Started: 7/27/2011 10:20 AM Replies: 1

7/27/2011, 10:20 AM
|
Joined 6/10/2011
Last visit: 5/8/2013
Posts: 1
Rating:
(0)
|
(0)
|
hello I need your help, I 2 ASCON M5 regulator, a manager and a DX ASCON PLC S7 300 simens I want to play in both variabre ASCON by the PLC on the DX attraver manager
my problem and my configuration ASCON DX manager in the PROFIBUS
if you like it, how I can configure the DX manager in the PROFIBUS network and read the temperature by plc via DX manager?
|
|
|
|

7/27/2011, 12:42 PM
|
Joined 3/21/2006
Last visit: 5/21/2013
Posts: 9063
Rating:
(820)
|
(0)
|
Hello,
In order to use a profibus slave is needimng a GSD file. In Simatic Manager you should assign a Profibus address which must be the same as gataway configuration. All the settings is according to http://www.asconcorp.com/library/pdf/delta2/DX_Programming.pdf There you should assign where will be send the temperature (which word/byte) in order Profibus Master (S7-300) to know where to read it.
Best regards, Hristo Mihalev
|
|
|
|