can i convert to d7-sys

Thread Starter: ahmadhani   Started: 11/5/2009 12:07 AM   Replies: 1

« Previous thread Next thread »
Page 1 of 1 (2 items)
  11/5/2009, 12:07 AM
Joined 11/4/2009
Last visit: 11/23/2009
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
i have simadyn d system with cpu  pm6 i use struc g and l  is it  easy to use d7-sys with  cfc  or it will be problem in converting
and if i convert what will i need to do that
Top
  11/6/2009, 7:47 AM
Joined 11/21/2007
Last visit: 11/24/2009
Posts: 214
Rating:
Rated: Outstanding [3.83 out of 5 / rated 6 time(s)]. (6) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Ahmadani

Guess you won't know until you try !!

Here are some limitations of Struc-G to D7 convertor ( As given by Miami against one of my previous posts ) :

The converter has some limitations:
- converts only 32bit Programs (no problem for you)
- converts only the standard libaries (FBS...) -> Check what libraries your project uses
- converts one FB-Editor page to four CFC pages of a CFC chart.

If your program uses only standard libraries, I guess there should be no major issues.

Good Luck
Navnag

There is no such thing as the last bug in a program
There are no stubborn bugs, There are only stubborn Debuggers.