Raw value for a Analog Channel
Thread Starter: S K Rewliya Started: 9/21/2009 9:35 PM Replies: 1

9/21/2009, 9:35 PM
|
Joined 12/27/2007
Last visit: 1/27/2012
Posts: 13
Rating:
(1)
|
(0)
|
Hi New to Quadlog system,please tell me how to see the raw value (mA of the Input)of an analog Input in a CAM card.I m using 4-mation 4.52 MBUS. It`s quite easy in S7,but here I have no idea. Thanks in advance. Regards, SKR
=== Edited by S K Rewliya @ 9/21/2009 9:37 PM [GMT ] ===
|
|
|
|
|

9/29/2009, 4:21 PM
|
Joined 12/20/2005
Last visit: 4/23/2013
Posts: 78
Rating:
(3)
|
(0)
|
Hello SKR,
Unfortunately QUADLOG does not support displaying the raw data value. You could convert the conditioned signal back to mA using a SCALER function block by configuring the engineering in low (EINL) and high (EINH) softlist parameters of the FB to your engineering range (0 - 100% for ex.) and the engineering outs (EOUTL and EOUTH) to 4 and 20 respectively.
Best regards, RJP
|
|
|
|