Hi all, i encounter a Simatic Panel OP77A that freeze at "Start" cursor after every power ON (after bootloader), refer attachment. It does not even want to respond on the UP and Down key. This situation happen right after a 2 weeks plant shutdown.

Please advise.
Thanks in advance.

Attachment: Image018.jpg  (38 Downloads)

Top
  1/9/2009, 8:02 AM
Joined 5/28/2008
Last visit: 4/14/2013
Posts: 897
Rating:
Rated: Outstanding [3.43 out of 5 / rated 122 time(s)]. (122) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Wich software do you use?

maybe you need a hotfix or else...

regards
manfred
Top
  1/9/2009, 11:26 AM
Joined 1/9/2009
Last visit: 1/19/2009
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I am using WinCC flexible 2007 V1.2.0.0_1.55.0.1.
This panel have been operating for almost a year without problem.
With this current problem, i could not even perform another download to the panel with the same software.
The transfer stops at 'Preparing connection to the device...'
Top
  1/9/2009, 4:38 PM
Joined 5/28/2008
Last visit: 4/14/2013
Posts: 897
Rating:
Rated: Outstanding [3.43 out of 5 / rated 122 time(s)]. (122) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Then please try to install an new servicepack or hotfix.

got to this side

http://support.automation.siemens.com/WW/view/en/28882233

and try this...

regards
manfred
Top
  1/10/2009, 7:03 AM
Joined 1/9/2009
Last visit: 1/19/2009
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
After installing the hotfix 4. I still could not perform download or OS update, same problem.
Should i send the panel back to the manufacturer?
Top
  1/12/2009, 12:05 PM
Joined 10/19/2005
Last visit: 4/11/2013
Posts: 1462
Rating:
Rated: Outstanding [3.7 out of 5 / rated 96 time(s)]. (96) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

at first, i would try to make a "Reset to factory settings" (not "os update"!).
For this you need a "null modem wire"
Look to this FAQ

-> http://support.automation.siemens.com/WW/view/en/19701610

When this does not help, then you should send the panel to repair,

regards,

Top
  4/5/2012, 4:05 PM
Joined 4/5/2012
Last visit: 4/5/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I also have the same problem with OP77A, What is "null modem wire".
Can you please give me the configuration.
Top
  4/5/2012, 5:10 PM
Joined 4/22/2010
Last visit: 5/18/2013
Posts: 3190
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

A null modem cable is a RS232 cable with TX and RX crossed at one end.

In case off op77a you have no RS232 only RS 485.

Have a look at the manual for more details :
http://support.automation.siemens.com/WW/view/en/21084916

Regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!