  5/8/2012, 12:18 PM
Joined 3/1/2011
Last visit: 7/4/2014
Posts: 16
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
MASTER DRIVE 6SE7031-2EF60

DRIVE IS TRIPING IN FAULT F023

WHEN I AM WATCHING IN r949 i is showing some times 1 and some times 2
1 mean high temp
2 mens wire break

I check the wire but no wire break and loose connection found in drive.

when after all , switched on drive and checked the temp found 29 C. r833

room ac is in panel room which is maintaining 25 c. room temprature.
drive is triping 2 to 3 times in 24 hours

55kw  drive

at which temp it will give alarm of F023

and i want to know what are the posible cause for this temp sensor faulty,wire loose ,or card problem what i should do solve this problem .

with thanks
your dear friend.



=== Edited by herish @ 5/8/2012 12:36 PM [GMT ] ===


Top
  5/8/2012, 4:30 PM
Joined 9/7/2010
Last visit: 10/17/2014
Posts: 230
Rating:
Rated: Excellent [4.73 out of 5 / rated 33 time(s)]. (33) 
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
herish wrote:
MASTER DRIVE 6SE7031-2EF60

DRIVE IS TRIPING IN FAULT F023

WHEN I AM WATCHING IN r949 i is showing some times 1 and some times 2
1 mean high temp
2 mens wire break

I check the wire but no wire break and loose connection found in drive.

when after all , switched on drive and checked the temp found 29 C. r833

room ac is in panel room which is maintaining 25 c. room temprature.
drive is triping 2 to 3 times in 24 hours

55kw  drive

at which temp it will give alarm of F023

and i want to know what are the posible cause for this temp sensor faulty,wire loose ,or card problem what i should do solve this problem .

with thanks
your dear friend.


According to manual you should check following things:

1.whether the fan -E1 is connected and is
rotating in the correct direction
2.that the air entry and discharge openings are
not restricted
3. temperature sensor at -X30


Check after changing sensor..whether drive is working ok or not

Regard
Deep Bhatt

"The art of being wise is knowing what to overlook"
Top
  5/9/2012, 7:50 AM
Joined 7/8/2009
Last visit: 10/17/2014
Posts: 1891
Rating:
Rated: Excellent [4.18 out of 5 / rated 447 time(s)]. (447) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
just a silly thing,

Also check dusts on your cards

Sometime cleaning of drive does the Job in such cases

I dont Like people driving Fast, thats the reason I overtake them ;)
Top
  5/17/2012, 2:58 AM
Joined 6/13/2006
Last visit: 10/3/2014
Posts: 194
Rating:
Rated: Excellent [4.83 out of 5 / rated 6 time(s)]. (6) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
herish wrote:
MASTER DRIVE 6SE7031-2EF60

DRIVE IS TRIPING IN FAULT F023

WHEN I AM WATCHING IN r949 i is showing some times 1 and some times 2
1 mean high temp
2 mens wire break

I check the wire but no wire break and loose connection found in drive.

when after all , switched on drive and checked the temp found 29 C. r833

room ac is in panel room which is maintaining 25 c. room temprature.
drive is triping 2 to 3 times in 24 hours

55kw  drive

at which temp it will give alarm of F023

and i want to know what are the posible cause for this temp sensor faulty,wire loose ,or card problem what i should do solve this problem .

with thanks
your dear friend.


Hi,
I had seen this fault long time ago, after I exchange the new power board, problems solved.

Regards
chook


Top
  5/18/2012, 6:35 PM
Joined 9/13/2011
Last visit: 10/12/2014
Posts: 29
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear friend

we have the same problem and we found that the IMPI (IVI) card is the cause of thi fault
Top
  5/22/2012, 1:40 PM
Joined 5/16/2012
Last visit: 6/10/2014
Posts: 12
Rating:
Rated: Outstanding [3.75 out of 5 / rated 8 time(s)]. (8) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Dear Herish,

Do you have any sensor for measuring the winding temperature of motor and it is linked with the drive input?

if it is so, try to remove that connections and check the same problem is repeating.

 

Top
  8/22/2012, 9:13 PM
Joined 9/13/2011
Last visit: 10/12/2014
Posts: 29
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Dear friend

we face this problem and we found the ivi(impi) card was the reason
try replace it

regards

Top
  8/22/2012, 10:29 PM
Joined 6/4/2008
Last visit: 10/17/2014
Posts: 970
Rating:
Rated: Excellent [4.41 out of 5 / rated 239 time(s)]. (239) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi, I have to agree, it is most likely to be the IVI card, unless the sensor wire is degraded.
Depending on your technical level, you can experiment using a 10k potentiometer wired/connected to the IVI at X31 pins 1 & 2, at full resistance (i.e. 10kohms), this will simulate 25 degrees (approximately)

As the resistance is reduced (simulating temperature increase), the drive should trip on F023.
You cannot change the trip level, this is set in the firmware for the drive type (P070).

If you have a communication network on the drive, you can trend K0247, this should indicate whether the temperature is rising slowly (real temperature), or a sudden temperature spike (hardware problem).

Hopefully this gives some pointers.
Regards,
Graeme

There are 10 types of people . . .
Those who understand Binary, and those who don't.
Top
  7/22/2013, 4:49 PM
Joined 9/1/2005
Last visit: 10/17/2014
Posts: 2813
Rating:
Rated: Excellent [4.02 out of 5 / rated 129 time(s)]. (129) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
new question split to a seperate thread with the subject MASTER DRIVE FAULT F023 - disable the slideshow tripping of drive by this failure.

Best regards
CS Moderator
Top
  7/25/2013, 3:51 PM
Joined 6/18/2012
Last visit: 7/25/2013
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Regard,

please, I have a problem with MasterDrive of Centrifuge BMA, I change the IVI board and the power supply and on the F23, please help me with this case.
also connect a resistor, the fault is intermittent

I hope your answer