Hi Rich, as I stated, the archive that I attached works fine, perhaps if you uploaded your archive, I can compare and find the differences between my configuration and yours.

Regards,
Graeme

There are 10 types of people . . .
Those who understand Binary, and those who don't.
Top
  5/31/2012, 10:08 PM
Joined 10/9/2008
Last visit: 3/26/2013
Posts: 22
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Graeme

I found the problem grin it was not related to the drive parameters but the Profibus control word from the PLC. Setting of Bit 0 of the control word was being conditioned on bit9 of the status word. This bit9 is low whenever P700 is not set to 6.
I should have checked the PLC code earlier but as the same FB was being used to control the MM440 ok, I presumed it was the MM420 parameters.
Note:  It worked ok with the MM440 because of how the multiple comand data sets have configured on the MM440.

Thanks to everybody who responded 
Top