Dear sir,
we have a Siemens Master Drive MC (MLFB:6SE7021-3TP70) Serial no:F2B7015041. it is shows the error F002 drive stop working, when i press the 'P'on the drive 'PUM' for 2sec error will gone after drive is works, but this condition is repeated when i switch on the machine mains power supplay.

 

Top
  5/20/2012, 6:54 PM
Joined 7/8/2009
Last visit: 5/17/2013
Posts: 1167
Rating:
Rated: Excellent [4.25 out of 5 / rated 326 time(s)]. (326) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
F002 - Precharging Fault - The monitoring time of pre-charging has expired, i.e. the DC link voltage has not reached the setpoint within 3 secs

Now, Check DC voltage physically on DC terminals as well as in parameter

Normally, this fault comes when you dont have DC link charged and you trying to give start command

Also try searching F002 using search function and you will find lots of discussion regarding this

Following may be help you more

Common Faults in Masterdrives and their solutions

problem with F002. (DC Inverter SIMOVERT VC6SE7041-2WL60-Z).

Regards,
Devesh Vithani



=== Edited by Vithani @ 5/20/2012 7:09 PM [GMT ] ===



Please say Thanks if your Problem is Solved.. :-)
Top
  5/22/2012, 5:46 PM
Joined 11/1/2011
Last visit: 3/8/2013
Posts: 58
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
thanks
Top
  6/5/2012, 9:12 AM
Joined 11/1/2011
Last visit: 3/8/2013
Posts: 58
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Vithani wrote:
F002 - Precharging Fault - The monitoring time of pre-charging has expired, i.e. the DC link voltage has not reached the setpoint within 3 secs

Now, Check DC voltage physically on DC terminals as well as in parameter

Normally, this fault comes when you dont have DC link charged and you trying to give start command

Also try searching F002 using search function and you will find lots of discussion regarding this

Following may be help you more

Common Faults in Masterdrives and their solutions

problem with F002. (DC Inverter SIMOVERT VC6SE7041-2WL60-Z).

Regards,
Devesh Vithani

Dear sir,

    Earlier disscusion of F002, that problem is not solved, what i do ? need a repair for the drive? or it can be solve any parameter adjusted? give me best way sir.
Top
  6/21/2012, 11:06 AM
Joined 7/8/2009
Last visit: 5/17/2013
Posts: 1167
Rating:
Rated: Excellent [4.25 out of 5 / rated 326 time(s)]. (326) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
You check first whether it is drive or something out side. For this, give direct supply to the drive input termianals - 3 phase if it is converter or DC if it is inverter module

Then check DC votlage in parameter r006. If voltage is OK then your drive seems to be OK, and if voltage is not showing, you need to repair your drive.

In case of Inverter,most of the time its just a Fuse connected near DC bus so you can replace it if this is the case

Regards,
Devesh

Please say Thanks if your Problem is Solved.. :-)
Top
  6/21/2012, 4:57 PM
Joined 8/8/2011
Last visit: 5/19/2013
Posts: 120
Rating:
Rated: Outstanding [4 out of 5 / rated 25 time(s)]. (25) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Sir,

The Siemens Master Drive MC (MLFB:6SE7021-3TP70) Serial no:F2B7015041 you are describing is a Compact PLUS DC-AC inverter unit which normally gets its DC link voltage from a rectifier unit similar to attachment or a DC Link Module.

The "TP" in part number provides this indicator by part number. 

If there are other drives using the same DC power bus and they are operating properly then most likely the 6SE7021-3TP70 will need to be repaired or replaced.  Note: If replacement path taken, this drive likely has options mounted in slots A, B, and/or C  which will need to be reused or replaced as well.  Also, if using Functions technology software (F01) would need to purchase this option for a replacement.

If this drive is only drive being powered by DC link voltage supplier then the DC link voltage supplier or possibly some hardware interface such as fuses must be replaced. Verify it is providing the DC link voltage.

Rectifier Unit Part Numbers (common supplier of DC link)
6SE7024-1EP85-0AA0
6SE7031-2EP85-0AA0
6SE7032-3EP85-0AA0

DC Link Module (possible supplier of DC link)
6SE7090-0XP87-3CR0

Deputy

Attachment: MASTERDRIVES MC DC Bus.pdf  (36 Downloads)

Top
  6/21/2012, 5:42 PM
Joined 11/1/2011
Last visit: 3/8/2013
Posts: 58
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Deputy schrieb:
Dear Sir,

The Siemens Master Drive MC (MLFB:6SE7021-3TP70) Serial no:F2B7015041 you are describing is a Compact PLUS DC-AC inverter unit which normally gets its DC link voltage from a rectifier unit similar to attachment or a DC Link Module.

The "TP" in part number provides this indicator by part number. 

If there are other drives using the same DC power bus and they are operating properly then most likely the 6SE7021-3TP70 will need to be repaired or replaced.  Note: If replacement path taken, this drive likely has options mounted in slots A, B, and/or C  which will need to be reused or replaced as well.  Also, if using Functions technology software (F01) would need to purchase this option for a replacement.

If this drive is only drive being powered by DC link voltage supplier then the DC link voltage supplier or possibly some hardware interface such as fuses must be replaced. Verify it is providing the DC link voltage.

Rectifier Unit Part Numbers (common supplier of DC link)
6SE7024-1EP85-0AA0
6SE7031-2EP85-0AA0
6SE7032-3EP85-0AA0

DC Link Module (possible supplier of DC link)
6SE7090-0XP87-3CR0

Deputy

Dear sir,

      Am checked DC fuse link of the drive inside am found normal ok, i have doubt about F002 is this error is invertor section fault are control card in A,B,C  problem?
Top
  6/22/2012, 3:55 PM
Joined 8/8/2011
Last visit: 5/19/2013
Posts: 120
Rating:
Rated: Outstanding [4 out of 5 / rated 25 time(s)]. (25) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear putta,

Option boards in slots A, B, and C would not be cause of this fault since they only provide such functions as additional input/output terminals, communications, and encoder feedback interface for drive operation.

For your drive part number 6SE7021-3TP70, specifically need to check supply voltage for drive to identify where problem starts.  See attachment from hardware manual where DC link is present at top of drive under protective cover. When looking at drive with cover open:
 Bar 3 is in back    PE3 Protective conductor connection
 Bar 2 is in middle  DC link voltage -
 Bar 1 is in front DC link voltage + 

Assuming the AC input supply voltage is 415 VAC Three Phase, then DC voltage to the drive should be approximately 415 * 1.35 = 560 VDC.

If dc voltage across the DC terminals of the drive with voltmeter is not approximately 560 VDC, then the fault is caused by issue somewhere in incoming supply upstream of individual drive (i.e. rectifier, contactor, AC input supply fuse, circuit breaker, etc.) 

If you measure the dc voltage across the DC terminals of the drive with a voltmeter the voltage is also as per the specification (approx 560V dc) but still the drive trips with this F002 fault. You have to now check the value of r006 and compare it with what your voltmeter reading at the same instance. If the values do not match ( you will find the value of r006 is 0v or very much lower than the actual voltage measure by the voltmeter) the drive will trip with F002. What happens here is the actual dc voltage is correct but the DC measuring  circuit is not measuring the voltage correctly and the microcontroller feels that the required voltage is not reached and trips the drive with F002.
This would indicate that the 6SE7021-3TP70 drive itself needs to either be repaired or replaced as there is not a spare part sold seperately for field exchange to attempt repair.

Best Regards,

Deputy

Attachment: dc link mc drive p.pdf  (38 Downloads)

Top
  6/29/2012, 2:26 PM
Joined 11/1/2011
Last visit: 3/8/2013
Posts: 58
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Deputy wrote:
Dear putta,

Option boards in slots A, B, and C would not be cause of this fault since they only provide such functions as additional input/output terminals, communications, and encoder feedback interface for drive operation.

For your drive part number 6SE7021-3TP70, specifically need to check supply voltage for drive to identify where problem starts.  See attachment from hardware manual where DC link is present at top of drive under protective cover. When looking at drive with cover open:
 Bar 3 is in back    PE3 Protective conductor connection
 Bar 2 is in middle  DC link voltage -
 Bar 1 is in front DC link voltage + 

Assuming the AC input supply voltage is 415 VAC Three Phase, then DC voltage to the drive should be approximately 415 * 1.35 = 560 VDC.

If dc voltage across the DC terminals of the drive with voltmeter is not approximately 560 VDC, then the fault is caused by issue somewhere in incoming supply upstream of individual drive (i.e. rectifier, contactor, AC input supply fuse, circuit breaker, etc.) 

If you measure the dc voltage across the DC terminals of the drive with a voltmeter the voltage is also as per the specification (approx 560V dc) but still the drive trips with this F002 fault. You have to now check the value of r006 and compare it with what your voltmeter reading at the same instance. If the values do not match ( you will find the value of r006 is 0v or very much lower than the actual voltage measure by the voltmeter) the drive will trip with F002. What happens here is the actual dc voltage is correct but the DC measuring  circuit is not measuring the voltage correctly and the microcontroller feels that the required voltage is not reached and trips the drive with F002.
This would indicate that the 6SE7021-3TP70 drive itself needs to either be repaired or replaced as there is not a spare part sold seperately for field exchange to attempt repair.

Best Regards,

Deputy

Thank you sir.
Top
  8/18/2012, 10:55 AM
Joined 11/1/2011
Last visit: 3/8/2013
Posts: 58
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
putta wrote:
Deputy wrote:
Dear putta,

Option boards in slots A, B, and C would not be cause of this fault since they only provide such functions as additional input/output terminals, communications, and encoder feedback interface for drive operation.

For your drive part number 6SE7021-3TP70, specifically need to check supply voltage for drive to identify where problem starts.  See attachment from hardware manual where DC link is present at top of drive under protective cover. When looking at drive with cover open:
 Bar 3 is in back    PE3 Protective conductor connection
 Bar 2 is in middle  DC link voltage -
 Bar 1 is in front DC link voltage + 

Assuming the AC input supply voltage is 415 VAC Three Phase, then DC voltage to the drive should be approximately 415 * 1.35 = 560 VDC.

If dc voltage across the DC terminals of the drive with voltmeter is not approximately 560 VDC, then the fault is caused by issue somewhere in incoming supply upstream of individual drive (i.e. rectifier, contactor, AC input supply fuse, circuit breaker, etc.) 

If you measure the dc voltage across the DC terminals of the drive with a voltmeter the voltage is also as per the specification (approx 560V dc) but still the drive trips with this F002 fault. You have to now check the value of r006 and compare it with what your voltmeter reading at the same instance. If the values do not match ( you will find the value of r006 is 0v or very much lower than the actual voltage measure by the voltmeter) the drive will trip with F002. What happens here is the actual dc voltage is correct but the DC measuring  circuit is not measuring the voltage correctly and the microcontroller feels that the required voltage is not reached and trips the drive with F002.
This would indicate that the 6SE7021-3TP70 drive itself needs to either be repaired or replaced as there is not a spare part sold seperately for field exchange to attempt repair.

Best Regards,

Deputy

Thank you sir.

Dear sir, 

            If posssible to repaire master drives in my own electronics workshop? or send to SIEMENS service center?

with regards
rajesh.putta