All...I´m making a migration from S5 (CPU 115) to S7. The job has to be make only on weekends. So, before change all hardware, I want to test the S7 software, using the S5 I/O rack. After ensure that the S7 software is OK, I change all the hardware. My question: Witch S5 card I should use in order to make the S5 rack a profibus slave. I intend to remove the CPU and use a kind of card. I´ve already do this using an IM-318, for CPU 100U; but now, the CPU is 115. There are only digital input/outputs cards.
Top
  8/3/2012, 4:57 PM
Joined 7/15/2008
Last visit: 5/14/2013
Posts: 182
Rating:
Rated: Excellent [4.64 out of 5 / rated 11 time(s)]. (11) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Have a look at this pdf.


Attachment: HB37E_IM_306-1LE00_09-28.pdf  (68 Downloads)

Top
  8/3/2012, 6:07 PM
Joined 9/27/2006
Last visit: 5/19/2013
Posts: 3928
Rating:
Rated: Excellent [4.15 out of 5 / rated 619 time(s)]. (619) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Silva;
If you want to go the Profibus-DP route, you can use a IM 318C in the S5 rack, also for a S5-115U.
Have a look at this recent discussion, and follow the link provided by our friend Marcjan tosee some sample programs to configure ihe IM 318C.

https://www.automation.siemens.com/WW/forum/guests/PostShow.aspx?HTTPS=REDIR&PageIndex=1&PostID=392449&Language=en

If your s7 CPU is a S7-400, you also have the alternative of using an IM 463-2 modules that interfaces with S5 racks through an IM 314:

http://support.automation.siemens.com/WW/view/en/4069554

We have used it with great results when preparing our migrations from S5 to S7.

Hope this helps,
Daniel Chartier

Top
  8/3/2012, 7:46 PM
Joined 1/16/2012
Last visit: 4/27/2013
Posts: 4
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
 Hello Chartier...Tks for tips...You said I can use the IM-318 for 115 rack? I believe not, because IM-318 is for small CPU, like CPU 100-U.
I saw the link you suggest, but, as I understand, it is to communicate a S7 with S5 keeping the S5 CPU. I want to remove the S5 CPU. When I used an IM-318 replacing CPU 100-U, it was not necessary to use the Com Profibus to configure it. All configuration was done on Step 7.
Top
  8/3/2012, 9:54 PM
Joined 9/27/2006
Last visit: 5/19/2013
Posts: 3928
Rating:
Rated: Excellent [4.15 out of 5 / rated 619 time(s)]. (619) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Silva;
If it can be of any help, here is how the IM 308C is described in the ET 200U manual:

ET 200U Distributed IOs:
http://support.automation.siemens.com/WW/view/en/1142470 

1.4 Slaves in the ET 200 distributed I/O system
The following can be used as DP slaves in the distributed I/O system:
·          Distributed I/O stations: ET 200B, ET 200C, ET 200M, ET 200S,
·          ET 200X (up to 12 Mbaud) and ET 200U, ET 200L (up to 1.5 Mbaud)
·          Progammable controllers/automation systems, such as:
        –         S5-115U, S5-135U or S5-155U with IM 308-C as DP slave
        –         S5-95U with DP slave interface (up to 1.5 Mbaud)
        –         S7-300 with CPU 315-2 DP or CP 342-5 as DP slave
        –         S7-400 with CP 443-5 as DP slave
·          Interface to the actuator/sensor interface with the DP/AS-I link
·          Text displays and operator panels for local operator control and monitoring
·          MOBY identification systems
·          Low- voltage switchgear
·          Siemens or other-vendor field devices, 

IM 308-C (DP slave)
As of release status 3, the IM 308-C can be used as a DP slave in the S5-115U, S5-135U and S5-155U programmable controllers. This means, for example, that you can transfer data between two programmable controllers. I agree that the IM 308C is of a smaller format than the other S5-115U modules, but you would have used an Adapter Casing (Warning: this MLFB must be validated, I suggest you do a Support Request directly to Siemens with the link at the top right of this page): 6ES5 491-0LB11.

If you have experience programming the IM 308C as a DP slave already in earlier projects, and you feel you do not need configuration software such as Com Profibus, then go right ahead (and please write the procedure in a post on the forum as a guide for others to follow). But my recollections of the ET 200U was that there were parameters and internal addressing to be done with Com Profibus. In an case, do read the S7 master-IM 308C slave sample provided in Marcjan's earlier post and see if it can apply to your project.

Hope this helps,
Daniel Chartier
 



=== Edited by dchartier @ 8/3/2012 9:59 PM [GMT ] ===


Top
  8/6/2012, 7:30 PM
Joined 1/16/2012
Last visit: 4/27/2013
Posts: 4
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi...
I have experience using IM-318, not IM-308C. I have used the IM-318 replacing a 100-U CPU. The IM-318 has dip switch on it, and we configure one dip for DP protocol and other are for the address. Then, we configure this address on step 7 hardware configuration. No additional configuration is necessary on IM-318.
Now, I have to make the same job, but the CPU is not a 100-U, but a 115-U. My question is if there is any kind of card for 115_U, similar to IM-318 for 100_U...
Regards,

Silva
Top
  8/6/2012, 10:35 PM
Joined 9/27/2006
Last visit: 5/19/2013
Posts: 3928
Rating:
Rated: Excellent [4.15 out of 5 / rated 619 time(s)]. (619) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Silva;
As stated earlier, in order to use a S5-115U as a DP slave to a S7 PLC, you will need a IM 318C with an adaptor casing (please request the exact part number from Siemens); you might also have to look into using Com Profibus as shown in the earlier links.
Note that all S5 hardware is now dicontinued, so you might have to look for PLC repairshops on the web; Com Profibus I believe  Have a look at the following manual to give you an idea of the configuration of the IM 318C in a S5-115U rack, in slave mode:
COM PROFIBUS  
Com Profibus can still be obtained from Siemens on a spare parts basis:
http://support.automation.siemens.com/WW/view/en/5707508
Or you could ask on the forum, some members might still have a copy of the software and be willing to help you out.
Hope this helps,
Daniel Chartier
Top
  8/7/2012, 10:42 AM
Joined 10/7/2005
Last visit: 5/19/2013
Posts: 2353
Rating:
Rated: Excellent [4.26 out of 5 / rated 612 time(s)]. (612) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Silva_br wrote:
My question is if there is any kind of card for 115_U, similar to IM-318 for 100_U...

Hello Silva_br

yes there is and Daniel Chartier already supplied you with all the info on how a Siemens IM308C could be used for this.
The downside of the IM308C solution is that you must keep the 115 CPU in the rack which will need to be programmed to do the data marshalling between the IM308C Profibus I/O's and the local physical I/O cards in the 115 U rack.

If that is not your cup of tea, please have another look at the pdf attachment in legacy support's reply (even though the 306-1LE00 is not a Siemens card, it tends to do the job quite neatly based on my experience).

I hope this helps 

Cheers

fritz

The advice and opinion given in this thread is that of the author and does not necessarily reflect the views of I S Systems Pty Limited.
To find out how I S Systems can help you with your automation needs please visit www.issystems.com.au.
Top
  8/28/2012, 2:37 AM
Joined 1/16/2012
Last visit: 4/27/2013
Posts: 4
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Chartier,

I´ve followed the example program, adapting to my configuration, I mean, using a 115 Cpu on S5 side, and a 315 2DP/PN at S7 side. After record the memory card with ComProfibus, install on the IM 308C; and load the HW configuration on S7, the LED RUN on the IM308 goes ON, and LED BF Blinking. Is it necessary any kind of program (I mean FB) on the S5 or S7 PLC? Do you have a sample for ComProfibus using a CPU 115 instead of 135?

Regards,
Top