My FM458 stop suddently and S7 400 CPU is all right. It is an online project. Who can tell me which kind of reason can cause FM458 stop? Think you!
Top
8/7/2012, 7:43 AM
KSN
Joined 8/25/2006
Last visit: 5/18/2013
Posts: 898
Rating:
(85)
(0)
cohiba1966 wrote:
My FM458 stop suddently and S7 400 CPU is all right. It is an online project. Who can tell me which kind of reason can cause FM458 stop? Think you!
Hello.
First connect to FM458 (better via DUST1 interface), go to the CFC-menu 'CPU-Module Information' and copy from both tabs the diagnostic information. This can help to understand the problem of stop.
Top
8/7/2012, 7:50 AM
cohiba1966
Joined 3/31/2012
Last visit: 11/22/2012
Posts: 21
Rating:
(0)
(0)
There is no reason or code for stop in diagnostic information.
Top
8/7/2012, 8:13 AM
KSN
Joined 8/25/2006
Last visit: 5/18/2013
Posts: 898
Rating:
(85)
(0)
Could you post diagnostics here?
What do you see in Module Information of FM, called from Simatic manger?
Have you activated checkbox 'Signal cause of STOP' in HWConfig-Properties of FM458-Diagnostic/Clock tab?
Top
8/9/2012, 2:02 PM
cohiba1966
Joined 3/31/2012
Last visit: 11/22/2012
Posts: 21
Rating:
(0)
(0)
KSN wrote:
Could you post diagnostics here?
What do you see in Module Information of FM, called from Simatic manger?
Have you activated checkbox 'Signal cause of STOP' in HWConfig-Properties of FM458-Diagnostic/Clock tab?
I find the message' Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP" '.
What is SFB20 stop ?
Top
8/10/2012, 5:44 AM
KSN
Joined 8/25/2006
Last visit: 5/18/2013
Posts: 898
Rating:
(85)
(0)
Hello.
SFB20 - Changing a Remote Device to the STOP State. Here is
manual
.
Top
8/15/2012, 8:39 AM
cohiba1966
Joined 3/31/2012
Last visit: 11/22/2012
Posts: 21
Rating:
(0)
(0)
I read the manual it seem that SFB20 can not cause FM458 stop. Is there any other reason for the stop of FM458-1DP? the attachment is the message of FM458-1DP. Thanks.
Attachment:
FM458 Diagnose.zip
(10 Downloads)
Top
8/15/2012, 10:58 AM
KSN
Joined 8/25/2006
Last visit: 5/18/2013
Posts: 898
Rating:
(85)
(0)
The main possible reason for FM458 STOP, that I could see in you diagnostic are events 48, 53 and 58. "User program canceled (stop due to system error) and "H" flashes on the display".
manual wrote:
Remedy:
Call-up the module information in the CFC and read-out the exception buffer.
H - fatal system error. What is the status of FM LEDs?
Go to the CFC-menu 'CPU-Module Information' and copy from both tabs (Error fields and Exception buffer) the diagnostic information.
Top
8/16/2012, 10:20 AM
cohiba1966
Joined 3/31/2012
Last visit: 11/22/2012
Posts: 21
Rating:
(0)
(0)
Only UF lamp flash. That is perhaps there is USF block in CFC. USF block is written with code 16#8000 which is used in software protection. Is that the reason?
Top
8/16/2012, 10:38 AM
KSN
Joined 8/25/2006
Last visit: 5/18/2013
Posts: 898
Rating:
(85)
(0)
cohiba1966 wrote:
Only UF lamp flash. That is perhaps there is USF block in CFC. USF block is written with code 16#8000 which is used in software protection. Is that the reason?
Standard USF-FB has no software protection. It could not be the reason of FM stop.
Post here diagnostics from
CFC-menu 'CPU-Module Information' from both tabs (Error fields and Exception buffer).
Top
1
2
›
»
Page 1 of 2 (18 items)
Actions
Copy Link
To conference
Product Conferences
LOGO!
SIMATIC TDC, FM458, T400
SIMATIC S7
SIMATIC S5 / STEP 5
SIMATIC 505
Communication / Networks
Programming Devices
PC-based Automation
Industrial PC SIMATIC PC
Decentral Peripherie
Industrial Software
SIMATIC Addons / IT4Industry
Process Control Systems SIMATIC PCS 7
Process Control System - APACS+
Process Control System - QUADLOG
Teleperm M / WinCC-TM / PCS 7 - TM
Other Process Control Systems
Visualization
SINUMERIK / SIMODRIVES / MASTERDRIVES / SIMOTION / SINAMICS
SINUMERIK CNC automation systems
SIMODRIVE Converter system
SIMOVERT MASTERDRIVES
Motion Control System SIMOTION
SINAMICS
MICROMASTER
ROBICON Perfect Harmony - Medium voltage converters
DC converters SIMOREG
SIMOTICS
Drive Tools
Process Instrumentation / Analytics / Weighing Systems SIWAREX
SIMATIC Ident
Low-Voltage Controls
Building Technology
General Conferences
Quick Links
All Conferences
The new Threads
Highlight Threads
Contact
Support Request
Contacts Worldwide
Moderator
Users online
Omarin89
,
dchartier
Help
Online Help
Guided Tour