Whenever I want to download OB1, OB2 and OB3 to Siemens S7-400 414-2XJ00-0AB0, only OB1 proceeds, while OB2 and OB3 gets stuck with the following message: "(D20C) OB cannot be copied as the associated priority class does not exist)". I've absolutely no idea what's wrong here, could you help me out? Thanks.
Top
  8/3/2012, 10:58 AM
Joined 3/21/2006
Last visit: 6/19/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

From where do you want to copy them?

Best regards,
Hristo Mihalev
Top
  8/3/2012, 11:00 AM
Joined 8/3/2012
Last visit: 9/14/2012
Posts: 45
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I have them offline in my project under Blocks, now I'd like to transfer them to S7-400.
Top
  8/3/2012, 11:01 AM
Joined 3/21/2006
Last visit: 6/19/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
What are the symbolic names of those OBs?
Top
  8/3/2012, 11:03 AM
Joined 8/3/2012
Last visit: 9/14/2012
Posts: 45
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
OB1 is CYCL_EXC, while OB2 and OB3 symbolic names are empty.



=== Edited by krneki10 @ 8/3/2012 11:04 AM [GMT ] ===


Top
  8/3/2012, 11:10 AM
Joined 3/21/2006
Last visit: 6/19/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
For what do you want to use them? Most probably you should change their number to corresponding OBs according supported of CPU. Check in hardware configuration->properties of CPU.

Best regards,
Hristo Mihalev
Top
  8/3/2012, 12:24 PM
Joined 1/28/2009
Last visit: 6/19/2013
Posts: 2921
Rating:
Rated: Excellent [4.1 out of 5 / rated 400 time(s)]. (400) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
krneki10 wrote:
OB1 is CYCL_EXC, while OB2 and OB3 symbolic names are empty.


Hello,
List of all possible OBs,their number and purpose of
using is mentioned in chapter1 of the following manual:


System Software for S7-300/400 System and Standard Functions Volume 1 and Volume 2

Best regards,