Hi
I have an analog Input module 2AI 6ES7331-7KB02-0AB0 
my question is: Can i connect two RTD (4L) to this module or one RTD (4L) sensor ?!!

Regards

George Awny
MATEC, Egypt
www.matecegypt.com
Top
  7/24/2012, 2:58 PM
Joined 9/27/2006
Last visit: 6/20/2013
Posts: 4037
Rating:
Rated: Excellent [4.16 out of 5 / rated 622 time(s)]. (622) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Gog;
As you can see from the attached illustration (from the S7-300 Module Data manual), you can only connect one RTD per 2 analog channels.
Hope this helps,
Daniel Chartier

Attachment: 331-7KB02.JPG  (11 Downloads)

Top
Thank you for this post from:
GOG
  7/24/2012, 3:21 PM
Joined 9/12/2011
Last visit: 6/12/2013
Posts: 29
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
dchartier wrote:
Hello Gog;
As you can see from the attached illustration (from the S7-300 Module Data manual), you can only connect one RTD per 2 analog channels.
Hope this helps,
Daniel Chartier

ya Dania ... you mean i can connect only one RTD in all cases ... 
thank you

George Awny
MATEC, Egypt
www.matecegypt.com
Top
  7/24/2012, 4:07 PM
Joined 9/27/2006
Last visit: 6/20/2013
Posts: 4037
Rating:
Rated: Excellent [4.16 out of 5 / rated 622 time(s)]. (622) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello George;
With the module you are using (AI 331-7KB02, 2 analog input channels with Resistsance temperature measurement) you can only connect 1 RTD.
If you had for example a AI 331-7KF02, 8 analog input, with Resistance temperature measurement, you could connect 4 RTD max (1 per 2 channels).
Hope this helps,
Daniel Chartier