Dear Experts,

      I have import Server Generated data and Run OS project editor on both Server and Client Station. I assign Start.pdl of Server to Start Picture of Client. After run Server, i follow activate Client.

     After that, Client Show picture of Start.pdl and then i moved mouse over on client, all picture goes away and only showing text "start.pdl". Please advise me any required steps. i have read related topics on forum and follow manual for server / client configuration but no succed. Thanks for any help in advance. please see attach for screen shot.   


sadsadsad

Attachment: Client Start Screen.pdf  (14 Downloads)

Bgrds,

Top
  7/19/2012, 12:49 AM
Joined 1/10/2008
Last visit: 6/20/2013
Posts: 2494
Rating:
Rated: Outstanding [3.77 out of 5 / rated 209 time(s)]. (209) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Is the client-server connection functioning?
Top
  7/24/2012, 1:50 AM
Joined 8/10/2011
Last visit: 6/15/2013
Posts: 61
Rating:
Rated: Excellent [5 out of 5 / rated 2 time(s)]. (2) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Phantom75 wrote:
Is the client-server connection functioning?


Hello Phantom75,

I think connection problem. I have generate server data and load it to client. share folder read/write access and Can ping each other are also no problem on both PC. Could you please show me to check client-server connection status? Thanks!!!

Bgrds,
Top
  7/24/2012, 11:58 AM
Joined 3/15/2010
Last visit: 6/17/2013
Posts: 128
Rating:
Rated: Excellent [4.4 out of 5 / rated 5 time(s)]. (5) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Please check the following items:
  • The Windows user exists in both client and server, and belongs at least to the group "SIMATIC HMI VIEWER"
  • The graphics runtime is active on the server (I believe this is needed if using OS project editor)
  • The "default server" is selected in the server data window

Good luck!