Hi,
I have a big problem, I have a Micromaster Vector that is set for analogue input and the front panel is disabled.I can't change any parameters because it is set for local control and I can't get throw from remote control.My question is DOES ANY ONE KNOW HOW TO RESET THE MICROMASTER VECTOR TO ITS DEFAULT SETINGS  MECHANICLY. I REPET, THE PARAMETER BUTTON DOESN'T WORK, ONLY ANALOGUE INPUTS 
Top
  6/13/2012, 12:06 PM
Joined 10/29/2007
Last visit: 4/24/2013
Posts: 651
Rating:
Rated: Outstanding [3.54 out of 5 / rated 41 time(s)]. (41) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
please set:
P009 (Parameter protection setting) = 3 =   All parameters can be read/set.

P007 (Keypad control) = 1 =   Front panel buttons can be selectively enabled or disabled depending on the setting of parameters P121 - P124. Note:     The digital inputs for RUN, JOG and increase/decreasefrequency are disabled.
P123 Enable/disable JOG button
P124 Enable/disable buttons


please check:
P051 to P055 and p356 Selection control function, DIN
- 13 = Disable the ability to change parameters
- 9 = local / remote via terminal


If you are using PLC-Control like USS or DP-Bus
pls. check / change P910 (Local / USS mode) and P928 (Local / Bus mode)

Mit freundlichem Gruß / Best regards

Jens S