Hi
i have a problem in Rectifier/Regenerating Unit, the PMU only shown numbers 6, and i can't change by pressing P or < >on PMU.please i would like know how to rectify this problem,
Hi
Is it showing Only 6 or F006?
For F006 -
Bus Over VDC link voltageThe unit was shutdown due to anexcessive DC link voltage.
Line voltage- | Shutdown threshold |
| range | |
| 380 V to 460 V | 835 V |
| 500 V to 575 V | 1042 V |
| 660 V to 690 V | 1244 V |
Now if it is Not F006, try Made Power On/OFF
Try replacing CUR if you have any in Spare
Are you able to connect it using Drive Monitor?