Technical Forum

SIMOTICS

catalog informations for 1PA6 Motors

Thread Starter: enku   Started: 8/3/2012 4:15 PM   Replies: 1

« Previous thread Next thread »
Page 1 of 1 (2 items)
  8/3/2012, 4:15 PM
Joined 3/25/2008
Last visit: 5/16/2013
Posts: 28
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello, at all.
I need informatios or catalog for this motor code 1 PA6 186-4HF03-0AA1, please.

Thanks you, enku
Top
  8/3/2012, 5:31 PM
Joined 8/8/2011
Last visit: 5/18/2013
Posts: 119
Rating:
Rated: Outstanding [4 out of 5 / rated 25 time(s)]. (25) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello enku,

For this motor 1PA6186-4HF03-0AA1 the 1PA6... motor product family was renamed under the 1PH7... motor product family name in 1999. 
Therefore almost all documentation available for any 1PA6 motor will be most readily available by using the converted name to 1PH7.
In this case the equivalent part number would convert as follows:
   Primarily, 1PA6 changes to 1PH7 plus the digit of the "4" changes to a "2" for definition of cooling type.  Also per below last digit can chagne as well, but this only defines the seals for flange and paint finish.

1PA6186-4HF03-0AA1 original motor
Catalog Description
COMPACT ASYNCHRONOUS MOTOR
FOR CONVERTER OPERATION
FORCED COOLING
DEGREE OF PROTECTION IP55
4-POLE WITH 400V MOTOR VLTG
WITH HTL SENSOR ROD 431
85KW,1750 RPM, 465NM
TERMINAL BOX TOP
CABLE ENTRY RIGHT
TYPE OF CONSTRUCTION IM B 35
STANDARD DESIGN
DEEP GROOVE BEARING
VIBRATION SEVERITY GRADE R
SHAFT/FLANGE ACCURACY GRADE R
SPLINE & HALFKEY BAL. WEIGHTS
AIR FLOW FROM DE TO NDE
ONLY PRIMED
SHAFT OUTLET IP 54



1PH7186-2HF03-0AA0 equivalent renamed motor
Catalog Description
SIMOTICS M
COMPACT INDUCTION MOTOR
74 KW, 1500 RPM, 471.1 NM,
VC: 85 KW, 1750 RPM, 463.8 NM,
173 A, VC: 172 A, W/O BRAKE;
WITH FAN, PG CABLE ENTRY;
REL. MOTOR ENCODER
HTL 1024 INCR/REV
TERMINAL BOX ON TOP, CABLE
ON THE RIGHT
DESIGN IM B35
BEARING F. COUPLING OUTPUT,
VIBRATION SEVERITY GRADE R,
SHAFT A. FLANGE ACCURACY GR. N
FITTED KEY + HALF-KEY BALANCING
AIR FLOW FROM DRIVE END TO NON-
DRIVE END
IP 55, FAN IP 54, PRIMED

Attached is catalog information for the 1PH7 from Configuration Manual for 400 V 3 AC line voltage in Servo Control mode.

Deputy
 
Top
Thank you for this post from:
Page 1 of 1 (2 items)
Actions