Hello,

Please, help me understand this..

L        KT 999.2
SD     T       1
A       T       1
=       M   254.1
L       T        1
T       MW250

I know that it means this:

- Start timer 1 (on-delay) with 999s.
- When time has elapsed turn on M254.1 and load current time value of T1 to MW250 as binary.

Here comes the question:

What time format will MW250 be loaded with...?

Always milliseconds...?
Or is it depending on the format I loaded the timer with..? In this case seconds...

Thanks in advance,

Regards Kristian
Top
  7/16/2012, 9:29 PM
Joined 12/22/2006
Last visit: 5/18/2013
Posts: 1295
Rating:
Rated: Excellent [4.01 out of 5 / rated 151 time(s)]. (151) 
Rated: Outstanding [4 out of 5 / rated 1 time(s)]. (1) 
Hello,
The value will be a number between 0 and 999
And in your example, in seconds (depends on time base)

If you would use LC T1, the value will be BCD coded (12 bits), between 0 and 999 in BCD this time.
And you would get the time base in bits 13 and 14