Hai All,

Please Anyone tell me the meaning of logic,

C DB 10
DO FW100
L DL 0
L FY9
!=F
=F100.0

If Anyone Having operating & Commissioning Manuals of WS 420-20 HMI,Please give a link..

Please Anyone give clarification on pointer DO.

Thanks&Regards,
Raj
Top
  7/14/2012, 1:35 PM
Joined 12/22/2006
Last visit: 5/18/2013
Posts: 1295
Rating:
Rated: Excellent [4.01 out of 5 / rated 151 time(s)]. (151) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

C DB10 just opens the datablock 10, telling that the next commands will use that from that block.

When executing the couple of instructions
DO FW100
L DL0

you do not load DL0, but the DL with the index specified in FW100.

Example:
If FW100 contains the value 8, you load DL8


The instructions
L FY9
!=F
=F100.0

check if the loaded value equals 9, and if true, flag F100.0 is set to "1". Else F100.0 is reset.




Best regards
jklm