3WL ACB communications with ION Enterprise Software from Schneider via Modbus communication

Thread Starter: Arif Hendrawan   Started: 5/13/2011 10:56 AM   Replies: 3

« Previous thread Next thread »
Page 1 of 1 (4 items)
  5/13/2011, 10:56 AM
Joined 5/13/2011
Last visit: 5/23/2011
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Sir,
How do the steps and how configuration 3WL ACB communications with ION Enterprise Software from Schneider via Modbus communication?
We get the problem can not read the ACB status to our ION Enterprise software.
Many thanks.
Arif Hendrawan



=== Edited by CS Moderator @ 5/14/2011 10:35 PM [GMT ] ===
new subject after splitting
Contact data deleted

Top
  5/13/2011, 5:04 PM
Joined 9/27/2006
Last visit: 5/22/2013
Posts: 3937
Rating:
Rated: Excellent [4.15 out of 5 / rated 619 time(s)]. (619) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Arif;
Is the ION software designed as a Modbus master (I do not know this system and might ask unseemly questions, but this is the kind of detail that is important). If so, what Modbus codes does it support? What type of communication interface does it require (and does the Sentron support the same, RS-232, RS-485...)?

How is the Sentron Modbus slave interface setup (address, baud rate, parity...)?

Here is a link to the Modbus communications manual for the Sentron 3WL. Please locate the ACB status you want to read in the Modbuis data map you will find there, so we can help you request it from your Modbus master.

https://a248.e.akamai.net/cache.automation.siemens.com/dnl_iis/zE/zE1Njc4NwAA_39850157_HB/SENTRON_WL_VL_circuit_breakers_with_communication_capability_MODBUS_EN_en-US.pdf

Hope this helps,
Daniel Chartier



=== Edited by dchartier @ 5/13/2011 5:05 PM [GMT ] ===


Top
  2/6/2013, 1:20 PM
Joined 5/2/2011
Last visit: 2/6/2013
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello
I have the same problem as Arif
ION Enterprise is a Modbus master, and support Modbus RTU or ASCII.
The software (ION Enterprise), use a 'driver' to know what modbus register have to read and write.

I read the system manual posted by dchartier, but I don't understand so well.

What i need is a modbus register map, with register in decimal format (better for me), for expample, at modbus adress 40963 is stored Current A.

I hope you can help me.

Thanks.

Marcos

Top
  2/6/2013, 2:02 PM
Joined 9/27/2006
Last visit: 5/22/2013
Posts: 3937
Rating:
Rated: Excellent [4.15 out of 5 / rated 619 time(s)]. (619) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello msalomone;
See if chapter 6 in the following manual provides the information you need:
System Manual SENTRON 3WL/3VL Circuit breaker
Remember that data exchanges allowed with the Sentron 3WL depend on the "Basic Type" selected.

Hope this helps,
Daniel Chartier