Dear sir 

          I have use 6RA7085-6DV62 drive for unwinder motor in Tention levller line but drive trip foult F030 ,during tripping drive current -16 to 18%, 

drive tripping resion not found pls help
Top
  8/10/2012, 9:12 AM
Joined 8/25/2006
Last visit: 5/21/2013
Posts: 898
Rating:
Rated: Excellent [4.2 out of 5 / rated 85 time(s)]. (85) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello.
What the fault value in r047.01?
Look at the following FAQ:
6RA70, SIMOREG DC Master; Unwarranted F030 with fault value 2.
 
Top
  8/10/2012, 11:02 AM
Joined 4/19/2012
Last visit: 4/24/2013
Posts: 8
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
KSN wrote:
Hello.
What the fault value in r047.01?
Look at the following FAQ:
6RA70, SIMOREG DC Master; Unwarranted F030 with fault value 2.

 


sir ro47.01 value is 2
Top
  8/10/2012, 11:09 AM
Joined 8/25/2006
Last visit: 5/21/2013
Posts: 898
Rating:
Rated: Excellent [4.2 out of 5 / rated 85 time(s)]. (85) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Look at mentioned FAQ and try to set U580 as suggested.
Top
  8/10/2012, 12:04 PM
Joined 4/19/2012
Last visit: 4/24/2013
Posts: 8
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
sir

        U580 not open due to  my drive is password protected by commissioning engg.and possword not found.
Top
  8/10/2012, 12:16 PM
Joined 3/21/2006
Last visit: 5/14/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

If this drive is still in commissioning phase discuss with engineer/s about that fault. In other case ask for password. Basically you should know it after commissioning. 

Best regards,
Hristo Mihalev
Top
  8/10/2012, 12:18 PM
Joined 8/25/2006
Last visit: 5/21/2013
Posts: 898
Rating:
Rated: Excellent [4.2 out of 5 / rated 85 time(s)]. (85) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
If you mean password protection in U005, U006 then ask him for password.
Another way is to reset all parameters to factory setting.
Top