Dear All,

I have 200 Kw (PM 240) Sinamics g120 drive having control card CU240 E-2 FIRMWARE VERSION 4.4.The setpoint is comming from  analog  source  in the form of 4-20 mA.

The customer demands that in case the setpoint falls below 4 mA ,the drive should run as per last setpoint.i wanted to know wheather this can be achieved or not.I know this can be achived in case of motorised potentiomter.but can it be done i case of Analog input . Can this realised throgh FFB. My scaling values are
4mA= 25% speed
20mA=100% speed 
Please Help , i want your help desparately

Regards
Top
  8/2/2012, 11:24 AM
Joined 10/29/2007
Last visit: 4/24/2013
Posts: 651
Rating:
Rated: Outstanding [3.54 out of 5 / rated 41 time(s)]. (41) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
see p0756 to p0760

an example you´ll find in FAQ http://support.automation.siemens.com/WW/view/en/5127160
it´s written for MM420 but can be used for G120 (without the 300Ohm resistor)

Mit freundlichem Gruß / Best regards

Jens S
Top
  8/2/2012, 12:06 PM
Joined 3/15/2011
Last visit: 5/20/2013
Posts: 52
Rating:
Rated: Outstanding [3.4 out of 5 / rated 5 time(s)]. (5) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
HiJen S
thanks for your prompt reply , but i have already commissioned the system ,it is running, but the customer is demanding that in case there is a wire brakage the the drive should run as per previou setpoint , im tring to implement this logic using FFB .Perhaps i can get help from your side too
Hope this explians my problem
Regards
Top
  8/2/2012, 3:27 PM
Joined 10/29/2007
Last visit: 4/24/2013
Posts: 651
Rating:
Rated: Outstanding [3.54 out of 5 / rated 41 time(s)]. (41) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
a explanation you will find in OPI chapter 6.4 Analog inputs; Table 6- 5      Parameters for the scaling characteristic and wire break monitoring http://support.automation.siemens.com/WW/view/en/61618946

or direct-link: https://www.automation.siemens.com/mdm/default.aspx?DocVersionId=42407973387&Language=en-US&TopicId=30400184587

Mit freundlichem Gruß / Best regards

Jens S
Top
  8/4/2012, 8:25 AM
Joined 3/15/2011
Last visit: 5/20/2013
Posts: 52
Rating:
Rated: Outstanding [3.4 out of 5 / rated 5 time(s)]. (5) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Jens S ,Thanks for your reply once again , i accomplised the task with the help of FFB .I'm attaching a copy so that i can be helpful for someone in future Rnf:lblSmileyTooltip_

Regards