is it possible to comm between IM151-8 PN cpu to CPU315PN via profinet?

if yes, which block we need (usend,urecv...?) and in netpro which comm. we need to add?
Top
  7/24/2012, 4:32 PM
Joined 6/17/2011
Last visit: 6/18/2013
Posts: 1360
Rating:
Rated: Excellent [4.09 out of 5 / rated 88 time(s)]. (88) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

I suggest to use s7-communication with the blocks BUT/GET or BSEND/BRECV.

You should also take a look in the compendium under http://support.automation.siemens.com/WW/view/en/20982954