I want to know  how to make Line topology for OLM G12. OLM "SYSTEM" LED blinks RED contniously though i had all setting on OLM DIP and terminate switch on Profibus connector.
Please suggest what can be the problem
Top
  7/14/2012, 12:49 PM
Joined 12/22/2006
Last visit: 5/18/2013
Posts: 1295
Rating:
Rated: Excellent [4.01 out of 5 / rated 151 time(s)]. (151) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

There is an FAQ with DIP settings:
http://support.automation.siemens.com/WW/view/en/50837578

On the most right and left OLM, I guess that you have one unused optical port.
For that unused port, I would set:
Mode bus without fiber-optic link monitoring
CH2 is set to this mode, when S1 is in position 1 and S2 is in position 0.
CH3 is set to this mode, when S3 is in position 1 and S4 is in position 0.

For the used optical ports, I would set:
Mode bus with fiber-optic link monitoring and segmentation
CH2 is set to this mode, when S1 and S2 are in position 0.
CH3 is set to this mode, when S3 and S4 are in position 0.

The electrical segments:
Mode electrical channel with segment monitoring
CH1 is set to this mode, when S0 is in position 0.

If you use recent devices only,
The default setting of S7 is position 0 (compatibility with older devices disabled).

Please note the following:

The OLM must be switched off when changing any setting. You can achieve this for

example by disconnecting the 5-pin terminal block.

Be also very sure that the Transmit and receive fiber-optic cables are swapped over.
There is an arrow near the connectors showing the sending/receiving fiber.

Furthermore, OLMs detect automatically the baudrate. For this, you should connect at least a Profibus Master on the bus and a slave (to generate traffic). From the manual:
Flashing red:
- There is no transmitting bus node
- No connection to a partner module sending frames
- Only one single bus node is connected, which only sends token to itself. After activation of a second bus node, the display must change (token frames are not enough to set the transmission rate)





=== Edited by jklm @ 7/15/2012 8:58 AM [GMT ] ===
Add FAQ http://support.automation.siemens.com/WW/view/en/50837578