M_syrian wrote:

  I have sinamics s-120 drive which BLM having  The BLM drive is some times tripping on the fault 30027 and some times it working ok and no fault msg diplay. please tell me the causes of this fault and guide me to how can I solve this fault>.please help me for this.

Top
  7/5/2012, 12:39 PM
Joined 6/15/2012
Last visit: 4/25/2013
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello friend, maybe that part of the manual can help you.


F30027 Power unit: Precharging DC link time monitoring

Drive object: All objects

Reaction: OFF2

Acknowledge: IMMEDIATELY

Cause: The power unit DC link was not able to be pre-charged within the expected time.

- line supply voltage too low.

- line supply phase fault.

- short-circuit or ground fault in the DC link.

- pre-charging circuit defective.

Fault value (r0949):

Missing internal enable signals, power unit (lower 16 bit):

(Inverted bit-coded notation FFFF hex -> all internal enable signals available)

Bit 0: Power supply of the IGBT gating shut down

Bit 1: Reserved

Bit 2: Reserved

Bit 3: Ground fault detected

Bit 4: Peak current intervention

Bit 5: I2t exceeded

Bit 6. Thermal model overtemperature calculated

Bit 7: (heatsink, gating module, power unit) overtemperature measured

Bit 8: Reserved

Bit 9: Overvoltage detected

Bit 10: Power unit has completed pre-charging, ready for pulse enable

Bit 11: STO terminal missing

Bit 12: Overcurrent detected

Bit 13: Armature short-circuit active

Bit 14: DRIVE-CLiQ fault active

Bit 15: Uce fault detected, transistor de-saturated due to overcurrent/circuit-circuit

Status, power unit (upper 16 bit, hexadecimal number):

0: Fault status (wait for OFF and fault acknowledgement)

1: Restart inhibit (wait for OFF)

2: Overvoltage condition detected -> change into the fault state

3: Undervoltage condition detected -> change into the fault state

4: Wait for bypass contactor to open -> change into the fault state

5: Wait for bypass contactor to open -> change into restart inhibit

6: Commissioning

7: Ready for pre-charging

8: Pre-charging started, DC link voltage lower than the minimum switch-on voltage

9: Pre-charging, DC link voltage end of pre-charging still not detected

10: Wait for the end of the de-bounce time of the main contactor after pre-charging has been completed

11: Pre-charging completed, ready for pulse enable

12: It was detected that the STO terminal was energized at the power unit

See also: p0210 (Drive unit line supply voltage)

Remedy: - check the line supply voltage

- check the line supply.

- line contactor was closed during the DC link fast discharge by the braking module, the pre-charging resistor must

cool down, check the interconnection of the external line contactor.

See also: p0210 (Drive unit line supply voltage)