F30027 Power unit: Precharging DC link time monitoring
Drive object: All objects
Reaction: OFF2
Acknowledge: IMMEDIATELY
Cause: The power unit DC link was not able to be pre-charged within the expected time.
- line supply voltage too low.
- line supply phase fault.
- short-circuit or ground fault in the DC link.
- pre-charging circuit defective.
Fault value (r0949):
Missing internal enable signals, power unit (lower 16 bit):
(Inverted bit-coded notation FFFF hex -> all internal enable signals available)
Bit 0: Power supply of the IGBT gating shut down
Bit 1: Reserved
Bit 2: Reserved
Bit 3: Ground fault detected
Bit 4: Peak current intervention
Bit 5: I2t exceeded
Bit 6. Thermal model overtemperature calculated
Bit 7: (heatsink, gating module, power unit) overtemperature measured
Bit 8: Reserved
Bit 9: Overvoltage detected
Bit 10: Power unit has completed pre-charging, ready for pulse enable
Bit 11: STO terminal missing
Bit 12: Overcurrent detected
Bit 13: Armature short-circuit active
Bit 14: DRIVE-CLiQ fault active
Bit 15: Uce fault detected, transistor de-saturated due to overcurrent/circuit-circuit
Status, power unit (upper 16 bit, hexadecimal number):
0: Fault status (wait for OFF and fault acknowledgement)
1: Restart inhibit (wait for OFF)
2: Overvoltage condition detected -> change into the fault state
3: Undervoltage condition detected -> change into the fault state
4: Wait for bypass contactor to open -> change into the fault state
5: Wait for bypass contactor to open -> change into restart inhibit
6: Commissioning
7: Ready for pre-charging
8: Pre-charging started, DC link voltage lower than the minimum switch-on voltage
9: Pre-charging, DC link voltage end of pre-charging still not detected
10: Wait for the end of the de-bounce time of the main contactor after pre-charging has been completed
11: Pre-charging completed, ready for pulse enable
12: It was detected that the STO terminal was energized at the power unit
See also: p0210 (Drive unit line supply voltage)
Remedy: - check the line supply voltage
- check the line supply.
- line contactor was closed during the DC link fast discharge by the braking module, the pre-charging resistor must
cool down, check the interconnection of the external line contactor.
See also: p0210 (Drive unit line supply voltage)