when I Display Real-Time Data, some Input display "UTRUE" in reverse yellow text, some Output display "BTRUE" in red text

Thread Starter: lbzu   Started: 7/1/2012 1:05 PM   Replies: 1

Next thread »
Page 1 of 1 (2 items)
  7/1/2012, 1:05 PM
Joined 12/5/2009
Last visit: 12/6/2012
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
In my system, when I Display Real-Time Data, some Input display "UTRUE" in reverse yellow text, some Output display "BTRUE" in red text. Could you please tell me what they mean? Thanks!



=== Edited by O_Moderator @ 7/3/2012 10:23 AM [GMT ] ===
new subject after splitting from question about quadlog

Top
  7/27/2012, 4:53 PM
Joined 12/20/2005
Last visit: 4/23/2013
Posts: 78
Rating:
Rated: Excellent [5 out of 5 / rated 3 time(s)]. (3) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

From APACS online help:
In 4-mation, input variables, output variables, and variables communicated from another ACM have an attribute called "quality".  Quality indicates the validity or certainty of a data value.  There are four possible data quality values:
 

· GOOD
· QUESTIONABLE
· UNAVAILABLE
· BAD


The quality is revealed by color and delimiter.  The display for each of these quality attributes is shown in the list below.
 

QUALITY                 DISPLAY COLOR       DELIMITER
 
GOOD                      CYAN (LIGHT BLUE)   NONE
QUESTIONABLE     YELLOW                       Q
UNAVAILABLE       YELLOW                       U
BAD                         RED                               B


If a value has bad quality, an error message is displayed instead of the bad data value.
 

Example: If a type is not stated when a function block needs to be typed (ANY type output is not wired to a typed input or variable) the ANY type output displays "B Tag not found"  in red.


If any quality other than GOOD is displayed, the problem should be investigated.  For example, if an input channel is reporting a value with a quality other than GOOD, the field transmitter may have failed.