Technical Forum

MICROMASTER

MM440-90 kW

Thread Starter: Arijit   Started: 6/20/2012 6:41 AM   Replies: 4

« Previous thread Next thread »
Page 1 of 1 (5 items)
  6/20/2012, 6:41 AM
Joined 7/12/2011
Last visit: 2/11/2013
Posts: 28
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
What should be the P1300 for a gas compressor commssioning.


Its urgent.plz help

Arijit
Top
  6/20/2012, 7:50 AM
Joined 7/8/2009
Last visit: 5/21/2013
Posts: 1167
Rating:
Rated: Excellent [4.25 out of 5 / rated 326 time(s)]. (326) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I guess you should set P1300=1 and P205=0

I have seperated some pages from Operating Instruction and Parameter List Manuals

Please refer them for more help

Regards
Devesh Vithani

Attachment: 440.zip  (6 Downloads)

Please say Thanks if your Problem is Solved.. :-)

Top
  6/20/2012, 10:38 AM
Joined 7/12/2011
Last visit: 2/11/2013
Posts: 28
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Thank Vithani for the reply.
But problem is when i start to run the motor inverter get tripped with F0003.
Can you give me any soluation?

Arijit

Top
  6/20/2012, 8:17 PM
Joined 6/4/2008
Last visit: 5/15/2013
Posts: 770
Rating:
Rated: Excellent [4.39 out of 5 / rated 225 time(s)]. (225) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi, a quick read of the OPERATING INSTRUCTIONS reveals that F0003 is an undervoltage Fault Rnf:lblSmileyTooltip_
Can you confirm that 415VAC is present on all supply phases, and that you have the correct DC Link voltage present (Approx Vin * 1.35)

Are you using a contactor inline with the supply, and is this being controlled correctly?
Regards,
Graeme

There are 10 types of people . . .
Those who understand Binary, and those who don't.
Top
  6/22/2012, 12:55 PM
Joined 2/22/2011
Last visit: 5/22/2013
Posts: 90
Rating:
Rated: Excellent [4.5 out of 5 / rated 2 time(s)]. (2) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
dear arijit
            please check the input voltage settings at the p210
            and input voltages to the drive at 3 phase

Thanks regards
ANBUGEETHAN GOWDA
Top
Page 1 of 1 (5 items)
Actions