I want to find out how i can run a motor to 60 hz ? what effects will be there if one runs a 50hz rated 400KW motor upto 60Hz?
Top
  12/22/2011, 4:42 PM
Joined 2/15/2010
Last visit: 5/2/2013
Posts: 257
Rating:
Rated: Above avarage [2.33 out of 5 / rated 3 time(s)]. (3) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear,
we tried before without drive with small power motor like 2,3kwatt and it burnt after 2 hours. but regarding high killowatt motor what i understood if we increase frequency we are going to increase speed over rated speed and this will reduce the power taken from motor because of rated killowatt at rated speed which achieved at 50 hz. but from mechanical viewpoint is it bearing will withstand overspeed due to 60hz?
Regards,

Hazem
Top
  12/22/2011, 4:47 PM
Joined 4/22/2010
Last visit: 5/22/2013
Posts: 3201
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
Hello,

I think it's all explained here : http://www.eng-tips.com/faqs.cfm?fid=1224

Regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!
Top
Thank you for this post from:
  3/17/2012, 12:56 PM
Joined 8/19/2010
Last visit: 5/4/2013
Posts: 9
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
In new conditions, if only frequency is going to change to 60Hz while voltages remaining same then please note that the designed o/p capacity would reduce to 83% of rated capacity.
However if supply voltage is also changing then please inform existing and new supply voltage conditions.
If the motor run at VFD application then NDE bearing should be insulated.

Top
  5/15/2012, 10:18 PM
Joined 6/4/2008
Last visit: 5/15/2013
Posts: 770
Rating:
Rated: Excellent [4.39 out of 5 / rated 225 time(s)]. (225) 
Users with special expertise supervising conferences
Rated: Excellent [5 out of 5 / rated 4 time(s)]. (4) 
Hi, the attached describes the effects for G120 and MM4 drives, but to be fair, this is applicable to any drive/motor combination.
Hope this answers some more questions.